What should I do on an existing concrete floor?
Last Post 04 May 2009 12:53 PM by BadgerBoilerMN. 3 Replies.
Printer Friendly
Sort:
PrevPrev NextNext
You are not authorized to post a reply.
Author Messages
snowmanfsUser is Offline
New Member
New Member
Send Private Message
Posts:6

--
23 Mar 2009 08:37 PM
My second floor is staple up hot water radiant but my basement has electric in the plan. I have an opportunity to change but I’m not sure what to do. Should I extend my hot water radiant system and add zones to the basement? If so what would you recommend above an existing concrete floor? This all assumes I find out from the builder that the floor was already insulated below... But it is new construction and is R-2000ish.
fullhouseUser is Offline
New Member
New Member
Send Private Message
Posts:4

--
01 May 2009 02:32 PM
From what I understand, hot water systems are far more efficient to run. You could certainly extend your radiant system (after speaking with a hydronics professional of course to ensure that your boiler system can handle it), securing the tubes either to wire mesh (which should be mechanically fastened to the concrete), and the tubing tied to the mesh, or use conduit clips (pre-drill holes and then use tapcons to secure the conduit clip over the tubing) followed by a 1 1/2" application of Therma Floor (gypsum underlayment) - Manufactured by Maxxon Corporation
Dana1User is Offline
Senior Member
Senior Member
Send Private Message
Posts:6991

--
04 May 2009 09:57 AM
Hydronic radiant in the floor will be more expensive to install up front, but will have HUGE flexiblity in heat source as future energy costs shift.

Unless you're in the land of 5cents/kwh electricity it's usually substantially more expensive to heat with electricity, and if you have electric resistance heating (low voltage or otherwise), you'll be locked into electricity as your heating source for that zone pretty much forever. Any change in heat source will have to overcome the cost hurdle of changing the heat distribution method, not just the heat source. With hot water radiant you can shift between gas/propane/oil/wood/electricity/solar without having to come up with a whole new heat distribution system.

Adding basement zones in an R2000 standards won't be a huge impact on the boiler sizing. Being earth-coupled, the basement is probably only ~5% of your heat load on "design-day", even if it accounts for 15-20% of your average heat load. Most boilers are oversized by 20-200% in the first place (let's hope a full heat-loss calc was done at the time it was specified/purchased.)

If it turns out the floor is not insulated, going with a radiant ceiling or low-temp panel radiators is still a decent way to go. (And electric radiant floor a TERRIBLE way to go.) If you can take the hit in headroom, adding even R5 (1") XPS under 0.75-1.25" of finish flooring (a ~2" loss of total headroom) is probably worthwhile. If you can take an even bigger hit, a radiant-embedded 2" slab or panel system (Warmboard, etc) over R5 XPS + finish flooring (2.5-4" loss of headroom) will still be cheaper to run than electricity in most markets. If you can get R10+ it'll still be cost-effective on the insulation part, but for every additional R5 you lose an inch of headroom.
BadgerBoilerMNUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:2010

--
04 May 2009 12:53 PM
My hero!!!!!!!!!!!!!
MA<br>www.badgerboilerservice.com