I'm leaning toward putting a Nuheat electric radiant flooring system beneath hardwood floors in part of a new home construction as a supplemental heat source in a bedroom and office for the Winter months.   I'm curious who out there has used Nuheat and what your experiences have been.    It'll be going under engineered flooring that will be glued down with Bostic's Best.   I'm wondering what affect it may have on the flooring over time if any.   It'll be coupled with their SOLO thermostats.
 
Any feedback much appreciated.


John

John A Gasbarre<br>Lamb Abbey Orchards<br>Union, ME 04862<br>[email protected]<br>
warmsmeallupUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:131
Avatar

--
24 May 2009 06:37 PM
Nuheat is a cable system that requires a mortar or thinset. Is that the planned substrate?
<a href="http://www.comfortradiant.com" target="_blank">COMFORT RADIANT HEATING, LLC</a><br> <a href="http://www.comfortradiant.com/zmeshinterior.php" target="_blank">Floor Warming</a><br><a href="http://www.comfortradiant.com/roof-deicing.php" target="_blank">Roof De-Icing</a><br><a href="http://www.comfortradiant.com/snow-melting.php" target="_blank">Snow Melting</a>
lambabbeyUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:148

--
24 May 2009 06:39 PM
Yup.   That's the plan.


John

John A Gasbarre<br>Lamb Abbey Orchards<br>Union, ME 04862<br>[email protected]<br>
BillNUser is Offline
New Member
New Member
Send Private Message
Posts:53

--
26 May 2009 10:18 PM
around me, electric is about 3 times the price than other fuels like propane oil, or gas. A real lot more expensive than wood.
Is electric cheaper in Maine? I pay about 0.12$/kwh in NJ.
Is the house completely electric?
lambabbeyUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:148

--
26 May 2009 10:52 PM
Bill:

Electricity is about the same here in Maine:  $0.12/kwh.   But I'd be using the Nuheat as optional zoned heat in the cold season, and just for a couple hours/day as needed within about a 330 sq ft area (office, bedroom and bath).   Primary heat source will be a small, centrally-located propane gas stove.   There will be no furnace or boiler.   The little house and adjacent barn will have a large solar PV system (15.3 kW) able to generate about 1,740 kWh/month, so I'll eventually be generating all of my own electricity.    The house itself is being built first with a small solar awning (6 - 225 kW panels), and then coupled with a much larger PV array on the eventual barn, similar to what you see HERE (62 - 225 kW panels).   

Note though that it's a small house (1,300 sq ft) and will have a heatload requirement of only around 12.0 kBTU/hr in the worst of Winter conditions because it's going to be very well insulated.  Regardless, I wouldn't be considering electric radiant heat in any capacity unless I were planning to generate the electricity to juice it.  


John

John A Gasbarre<br>Lamb Abbey Orchards<br>Union, ME 04862<br>[email protected]<br>
BillNUser is Offline
New Member
New Member
Send Private Message
Posts:53

--
27 May 2009 07:02 AM
I believe that it would be very hard to use the heat for a few hours per day. The wood above the elements is an insulator, so it will take a while to warm up. Energy will also flow down to heat the subfloor and srtucture below.
Another problem is the hardwood which does not like changes in temperature at all. The coefficient for expansion for wood is far greater than the heated mortar its setting on so the floor will be really creaky and could buckle or split. Radiant heat under wood is accepted and works within limits. One of those limits is a low rate of temperature change. This is why the Radiant Panel Assoc. recomends a constant flow reset loop.
NRT.RobUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1741

--
27 May 2009 08:50 AM
Bill, constant flow is nice, but I don't see anywhere that the RPA "recommends" that for wood floors. Also, electric elements should heat up fairly quickly.

John, why are you looking at mortar under wood? why not just use a mat that doesn't require that?
Rockport Mechanical<br>RockportMechanical.com
lambabbeyUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:148

--
27 May 2009 01:15 PM
Rob:

The Nuheat is an 1/8" mat that only requires about 1/8" of thincoat to install.   From what little I understand about the product, if it's installed with the right adhesive and thincoat there will be little if any problem with squeaky floors from expansion and contraction, as long as the wood flooring above it is engineered.    I'm open to other electric radiant mat systems, but most just look cheap, poorly made and with marginal controls.   I'm impressed with the Nuheat system.


BillN:

I'd be putting the Nuheat under a tiled bathroom on the first floor, but the vast majority of it would be on the second floor which has no direct heat source aside from the rising heat up the staircase from the floor below.  I would turn off the main heat source (the small propane stove on the first floor) at night, and just have the Nuheat heat up the bedroom for an hour or two in the evening and the office first thing in the morning, after which the propane stove would come back on as needed for the day.    Since I've got so much glass in the North-facing bedroom, I want to have an optional zoned heat source on a thermostat that would just heat a couple of specific rooms at night and early in the morning, rather than run the propane stove continuously to heat the whole house 24/7.



John

John A Gasbarre<br>Lamb Abbey Orchards<br>Union, ME 04862<br>[email protected]<br>
Dana1User is Offline
Senior Member
Senior Member
Send Private Message
Posts:6991

--
27 May 2009 03:56 PM
Somehow the notion of generating electricity at a net solar efficiency of 10-15% vs. solar-thermal for a net of 50% (at lower system cost) doesn't feel like the math is gonna work favorably, even when the higher cost of a hydronic radiant and solar thermal storage installation is included. Maybe it does, but I've not seen it work that way... yet.

But if the installed cost of PV crashes (as it should, given the low production cost of CIGS-technology PV) I may revisit those equations.

To be sure, a 12kbtu/h design-day heat load means the seasonal thermal requirements will also be modest (you may spend as many btus/year on heating hot water as on space heating, which would be very unusual in Maine.)
lambabbeyUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:148

--
27 May 2009 08:03 PM
Dana1:

I'm counting on the cost of PVs coming down over the next two years.    The small 6-panel solar awning on the house will go up in 2010, but the barn and its larger array not until 2011.    I'm guessing within two year's time, PV costs will be much more reasonable.    The tax incentives now available will help that much more.

I'd considered going with a wind turbine for the electricity, but the design of the barn and its Solar South facing roof just make it ideal for PVs.    Plus, it'll be silent and no one will see it but the birds.


Joh
n
John A Gasbarre<br>Lamb Abbey Orchards<br>Union, ME 04862<br>[email protected]<br>
NRT.RobUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1741

--
28 May 2009 07:54 AM
be careful if you consider wind. I believe a recent study has basically proven small turbines are a net energy loser, their effectiveness overall is directly related to their size.
Rockport Mechanical<br>RockportMechanical.com
lambabbeyUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:148

--
28 May 2009 10:32 AM
Rob:

I've written off the wind turbine at this point and am planning on going exclusively with solar.   

Plus, I'm not too keen on the idea of putting up a 60' lightning rod that's likely to get struck at some point at my expense.



John

John A Gasbarre<br>Lamb Abbey Orchards<br>Union, ME 04862<br>[email protected]<br>
warmsmeallupUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:131
Avatar

--
30 May 2009 05:46 PM

Zmesh low voltage elements are a slow growth heat. It doesn't require a mortar and it actuall will bring the wood up in temperature (never warmer than 85*) at the same rate as the element itself. Since the element is a bronze screen (9 or 12" wide), it comes with a 25 year warranty and you can nail your hardwood directly over (through) it without effecting the system (screen...holes..) .

I can send you some pictures of projects we've installed under exotics, short or wide plank, hard or soft woods.

Always maintain the woods' mositure content. Radiant or not, if you don't pay attention to it, you'll have problems.

In a correctly designed floor and system, you will see temperature changes in about 45 minutes.

<a href="http://www.comfortradiant.com" target="_blank">COMFORT RADIANT HEATING, LLC</a><br> <a href="http://www.comfortradiant.com/zmeshinterior.php" target="_blank">Floor Warming</a><br><a href="http://www.comfortradiant.com/roof-deicing.php" target="_blank">Roof De-Icing</a><br><a href="http://www.comfortradiant.com/snow-melting.php" target="_blank">Snow Melting</a>
warmsmeallupUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:131
Avatar

--
13 Jul 2009 02:22 PM
Your EnvironII looks interesting. Is it a foil? You show a pic with it in between layers of padding and carpet. What if (scenerio) a child pokes a metal object through the carpet?
<a href="http://www.comfortradiant.com" target="_blank">COMFORT RADIANT HEATING, LLC</a><br> <a href="http://www.comfortradiant.com/zmeshinterior.php" target="_blank">Floor Warming</a><br><a href="http://www.comfortradiant.com/roof-deicing.php" target="_blank">Roof De-Icing</a><br><a href="http://www.comfortradiant.com/snow-melting.php" target="_blank">Snow Melting</a>
Scott RUser is Offline
New Member
New Member
Send Private Message
Posts:2

--
13 Jul 2009 02:31 PM
I mistakenly discussed the EVII system for this application, that's why I removed it from the discussion. It is not designed to be used in any glue-down application, FYI.

Environ II panels are made of a pattern of a fixed-resistance heating element, “sandwiched” between two layers of aluminium foil laminate. The EVII system is controlled by a GFCI controlled thermostat in case something like this were to ever happen. To be honest, we haven't had this scenario.

Thanks for your note!
Just so you know, I work for WarmlyYours.<br>www.warmlyyours.com
warmsmeallupUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:131
Avatar

--
13 Jul 2009 02:41 PM
Is it a filament or a wire? What is the thickness? Is it repairable if damaged?
<a href="http://www.comfortradiant.com" target="_blank">COMFORT RADIANT HEATING, LLC</a><br> <a href="http://www.comfortradiant.com/zmeshinterior.php" target="_blank">Floor Warming</a><br><a href="http://www.comfortradiant.com/roof-deicing.php" target="_blank">Roof De-Icing</a><br><a href="http://www.comfortradiant.com/snow-melting.php" target="_blank">Snow Melting</a>
Scott RUser is Offline
New Member
New Member
Send Private Message
Posts:2

--
13 Jul 2009 02:58 PM
I believe this is getting a little OT, because the EVII system is not designed to be used in the application that lambabbey is discussing.

The EVII system uses an insulated wire, not a filament, for safety. It is 1/16" high. For reliability's sake, we do not recommend repairing it.

This concludes my OT banter. Sorry, lambabbey!
Just so you know, I work for WarmlyYours.<br>www.warmlyyours.com
Typhoon MarkUser is Offline
New Member
New Member
Send Private Message
Posts:1

--
17 Aug 2009 10:21 AM
Really it is a great experience to have a radiant floor heating beneath the floor, especially in cold climates. Recently I have renovated my home with heated floor mats, from then I feel pleasant at my home
Typhoon Mark
CarterSwingUser is Offline
New Member
New Member
Send Private Message
Posts:3

--
18 Sep 2009 07:02 AM
I think this get can be repaired once it is damaged. Nuheat mats and the cable system can be wired to any number of thermostats. So it is convenient too.
aka-noneUser is Offline
New Member
New Member
Send Private Message
Posts:1

--
02 Jan 2010 08:24 PM
By now you have likely made a choice, but for anyone who hasn't I can tell you that adding nuheat under our tile in the bathroom is great. I can keep the thermostat lower than I used to for that area but it still feels nice. What I liked over other options such as solar water and tubes is it is only ~1/16th inch thick. If I were building new then I'd do a boiler / solar and circulate hot water in the slab. But for existing installations this was not an option and I've been happy so far (~5 years). The tile installer had no problems with it and the added installation costs were minimal. I'm looking at adding it to a 20x30 space and also powering it with PV at least part of the day. This also removes my need for storage as I would be storing the soar as infloor heat. Again if I were starting from scratch I'd do in slab hot water but I'm not willing to cut my slab up or add a 2-3inch lift to my existing slab to add the tubes. If I were doing a space that had a raised floor then I'd consider adding the hot water heat in between the floor joists, but keep track of the weight of the water!