Posted By warmsmeallup on 07/19/2009 6:59 AM
Posted By Dana1 on 07/16/2009 3:57 PM
There's no heat lost going through 2 layers of wood, but the wood's insulating value (about R1/inch) limits the peak BTU/hour output (and the response time) the radiant can achieve in absolute terms.
Dana
I'm in agreement with the above floor installation being suggested. Presuming the design is R2 above and R30 below,
how does the R of the wood limit the peak btu output and at what reduced percentage?It the fundamental physics of the situation: The more R-value between the heating element (the hot water in the tubing) and the room air, the bigger the delta-T is required between conditioned space<-->heating water to get the same BTUs/hour across the R-barrier. Water being water, there's an absolute upper limit to the temperature you can use (called "boiling point of water".) There's no "percentage" to calculate unless you're comparing two independent R-values between heating element <-R-> room air.
The R-value of the insulation below the floor has no effect on how much heat you can get through the wood floor, but a HUGE affect on your heating bill. Since heat flows from warmer to colder, you want to limit heat flows into areas outside of the intended zone with big R-values between the heating element and the adjacent region.
If you're running with electric radiant you have a somewhat higher absolute upper limit on the heating element's temperature- called "kindling temperature of wood". ;-) (Most controls for electric radiant will keep it well under that temp.)