I have a large new build with in-floor radiant heat (20KW Thermolec electric mini Boiler - 2500 sq ft garage) I am going to use for a home gym. Question: Will 4 x 6 rubber mats 3/8" thick or so, or interlocking gymtype mat flooring allow heat to transfer through them, or will a rubber mat flooring decrease performance of the in-floor heat system. Thank You |
|
|
|
|
|
|
Full ICF Homes
 New Member
 Posts:73

 |
| 27 Apr 2011 09:07 AM |
|
Might there be a larger issue here. Dropping weights is not unusual in a gym setting so how about potential damage to the tubes? |
|
|
|
|
NRT.Rob
 Veteran Member
 Posts:1741
 |
| 27 Apr 2011 09:30 AM |
|
Rubber should be fine at that thickness, as long as the MFG indicates the product is ok over radiant (no offgassing smells, etc). |
|
| Rockport Mechanical<br>RockportMechanical.com |
|
|
Dana1
 Senior Member
 Posts:6991
 |
| 27 Apr 2011 09:32 AM |
|
Any foamed rubbery material will have an R-value, which will decrease the heat transfer at the same water temperature. But 10mm goods are probably no more than ~R2, and raisng the water temp ~10C would likely be sufficient to provide the same heat flux as the un-clad floor. |
|
|
|
|
NRT.Rob
 Veteran Member
 Posts:1741
 |
| 27 Apr 2011 10:16 AM |
|
Rubber is usually a low R-value material. We recommend foam and slab rubber products as carpet pads regularly. You're unlikely to exceed an R-1 for a 3/8" rubber product of any kind. |
|
| Rockport Mechanical<br>RockportMechanical.com |
|
|
Dana1
 Senior Member
 Posts:6991
 |
| 27 Apr 2011 10:39 AM |
|
Thanks Rob (I would have had to look it up, but I'm not surprised.) |
|
|
|
|
WI HANK
 New Member
 Posts:33
 |
| 27 Apr 2011 06:57 PM |
|
Thanks for the replys. Not worried about dropping weights; weights are rubber bumper plates dropped on a built up wood platform. |
|
|
|
|
BadgerBoilerMN
 Veteran Member
 Posts:2010
 |
| 02 May 2011 12:36 PM |
|
The radiant floor designer will input the floor coverings and may increase the design water temperature to account for the rubber, but as Rob suggests it will not be a deal breaker. Drop those weights buddy, if the slab won't stand up to it, the PEX tubing will be the least of your problems. |
|