Hydronic Heat with OWB system question
Last Post 22 Sep 2012 09:24 AM by idahohay. 3 Replies.
idahohayUser is Offline
21 Sep 2012 09:00 AM
My plan was to run water from my OWB directly to the slab using a mixing valve to reduce the temp to about 85 deg. The question is: since the PEX on a second floor apartment will be about five feet above the boiler which has a "pop off" that lets pressure out of the top of the tank at 2-3 psi., will it leak from the head pressure from the second story Pex? Mixing valves would allow me to run a different temp for under the second story sub floor. Is there any way to do this without a heat exchanger?
21 Sep 2012 03:07 PM
It's about 0.43 psi per foot of height, so yeah, if you have only 2-3 psi before the thing pops it's cork you're probably gonna leak, sooner or later. (5' x 0.42= 2.15 psi)
I'm surprised there's anything out there with such low pressure ratings, but I haven't looked at the specs for wood boiler stuff very closely.
BadgerBoilerMNUser is Offline
22 Sep 2012 08:28 AM
No.
Thanks BB, thats what I needed to hear . Now I'm thinking a brazed plate heat exchanger of the proper size.
Thanks for the reply.