Last Post 17 Nov 2012 11:01 PM by BadgerBoilerMN. 4 Replies.
Printer Friendly
Sort:
PrevPrev NextNext
You are not authorized to post a reply.
Author Messages
tomUser is Offline
New Member
New Member
Send Private Message
Posts:1

--
11 Nov 2012 01:09 PM

Im installing 1/2" pex for radaint heat under my floor . This is new construction so floor joises are open. the floor joises are TGI . I have 2 floors 1600 sq. ft. a floor with 9 cielings on 1st floor and 8 ft. cielings on 2nd. My question is should i hang the pex 3 inches or so off the bottom of the floor with hangers or use the alum. heat shealds to strap it directley to  the bottom of the floor? pro's and con's? I plan to use the double bubble foil insulation, should it be installed as close to the pex as possible or at the bottom of the joise creating a cavity?  I currentley have 1500 ft of radaint pex installed in the basement floor under concreat.   Hot water Heat supplied by a 250,000 btu outside central boiler corn/pellet stove.

Blueridgecompany.comUser is Offline
Advanced Member
Advanced Member
Send Private Message
Posts:656

--
11 Nov 2012 01:37 PM
Staple up with heat transfer plates making direct contact with underside of your sub floor 8" pattern 1/2 pex. Alternately you can install on top of your sub floor with RHT floor panel system or similar sandwich system.
Hanging pipe3 inches off sub floor in joist bay is a bad choice.
Dan
Dan <br>BlueRidgeCompany.com
NRT.RobUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1741

--
12 Nov 2012 10:49 AM
Skip the bubble insulation as well. use real insulation.
Rockport Mechanical<br>RockportMechanical.com
Dana1User is Offline
Senior Member
Senior Member
Send Private Message
Posts:6991

--
14 Nov 2012 05:37 PM
What they said. With suspended tube you'd have to run much hotter water (== higher distribution losses from your thermal store) and without better insulation you'd have next to no zone isolation between the basement (which is usually relatively low-loss) and the first floor (which has higher losses.)

Cheap R11 or R13 sound abatement batts snugged right up to the PEX/plates are usually sufficient for isolating zones, but if you want to run the basement 10F cooler than the first floor R19s are better.
BadgerBoilerMNUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:2010

--
17 Nov 2012 11:01 PM
3 inches? You have to admit, that is a new one. Where do they come up with this fiction. And, I thought everyone knew that bubble foil is a hoax.

http://www.healthyheating.com/Page%2055/Page_55_o6_bldg_sys.htm
MA<br>www.badgerboilerservice.com