My guess is this is a design feature WF wants for safety, or at least to cover their end of the liability in case there's a fire resulting from the Aux heating strips being powered without the ECM2 blowing.
Two distinct changes are made for the Envision with Aux heat strips, versus an Envision w/o the heat strips:
1.) Power for the ECM2 motor is wired to the Aux heat strips source power. In an Envision w/o heat strips power for the ECM2 motor is factory wired to the same power supplying the compressor.
2.) Power for the 240-to-24 VAC transformer is likewise changed to be connected to Aux heat strips power.
My guess is you could go into your unit and reconnect the balk/wh and gray/wh wires between unit power and the ECM2/transformer, but, my guess is you'd put yourself at an insurance risk if there were ever to be a fire, regardless of how the situation is rationalized.
I would think a better course of action is to leave power connected to the Envision as specified in the Installation Manual, including removal of the 2 wires noted in the above paragraph (Note 4 in the wiring schematic), and instead lock out Aux heat via a tstat setting, or tstat wiring change. In other words, make your adjustment on the low voltage side, via either tstat setting or tstat wiring.
Hope this helps.
Best regards,
Bill