One dealer sent me a plan to do the load calc on. 1800 sf main level, with about 1500 sf unconditioned basement.
From his info, the load came to 32,000 BTUh heating.
These people have a warm water spring (58 deg. year round, HIGH iron and some sulfur content, flowing approx. 50-75 gpm.) within 300' of the home. Because of the high iron and sulfur content, they didn't want an open loop. So, the recommendation, because of warmer ground (this is in Wyoming, which should have seen 45 deg. earth), was a 3 ton.
3 days ago, he calls me and tells me the heat pump is not heating the home. Two things happened. 1. He hadn't hooked up the auxiliary heat. It had been running on just geo, 100% of the time. 2. He hadn't verified that there was any insulation in the attic, and the windows are single pane aluminum frame. There's no insulation in the attic, at all. Plus, the walls are a log wall, framed and sheetrocked inside, with no insulation, and outside has aluminum siding, with no insulation. He had be told that it had R-19 batting (which is crappy insulation, but some is better than none).
So, upon recalculation, the load showed to be about 108,000 BTUh heating!! With the 10 kW strip heat, and the 3 ton heat pump, he was getting a max of 64-66K BTUh output.
The owner, a rich guy that knows better, apparently, refused to put any insulation in the attic to remedy the problem. He claimed that 2 other HVAC guys told him that would have no effect. Besides, the oil furnace (185,000 BTUh capacity) was enough to do it before. He figured the heat pump sucks and wanted it changed back to an oil furnace.
Then Friday, I got a call from this installer telling me that the owner changed his mind and decided to blow in an R-50 cellulose in the attic. This alone should drop the load of the house down to 48,000-54,000 BTUh.
Anyway, the system should perform a lot better, now that the home is insulated. |