Like most of you, I was pretty excited about the new tax credits. The more I dig into it, though, the more difficult it becomes for my home to qualify for those credits.
The two things working against me here are A) I want my heat to be delivered through radiant floors, so I need 65 kbtu/hr of hot water. B) My cooling load is much lower than the heating load - about 42 kbtu/hr for the cooling.
Item A is the killer. Just about every GSHP I can find that produces that volume of hot water is not Energy Star rated. The only one I can find is the Waterfurnace Synergy3D. (Enertech had several water-2-water pumps that were ES rated in January, but are no longer on the gov's list. What's up with THAT?!?!?)
Item B also bites me because the cooling capacity of the 6T Synergy is WAY above my needs. That forces me to buy a seperate AC or air-source heat pump.
Makes me want to slap every politician that passed this bill and ask them what they were thinking.
Anyway, sorry to bore you with the rant.
Here's my question:
Does anyone here know of another GSHP that will supply the hot water I need, and is Energy Star rated?
Thanks! |
|
|
|
|
|
|
pyropaul99
 New Member
 Posts:39
 |
| 19 Feb 2009 10:53 AM |
|
How about you insulate and draft seal to reduce your heating load to the point where you can use Energy Star equipment? Money spent on reducing your load requirements will keep paying back forever.
Paul. |
|
|
|
|
TechGromit
 Advanced Member
 Posts:535
 |
| 19 Feb 2009 11:23 AM |
|
Posted By hector8762 on 02/19/2009 8:37 AM
Makes me want to slap every politician that passed this bill and ask them what they were thinking.
Anyway, sorry to bore you with the rant.
I don't think requiring systems to have an energy star rating isn't an unreasonable request. Just because you want your system to operate in a particular matter doesn't mean we have to pay for it. |
|
|
|
|
tuffluckdriller
 Advanced Member
 Posts:610

 |
| 19 Feb 2009 11:47 AM |
|
Do you really think that ANY politicians were actually thinking concerning this bill? You really think they give a $#!^? .....
|
|
Clark Timothy (clark@pinksdx.com) VP sales, Tuff Luck Geothermal Drilling Geothermal Heat Pumps: Heating and Cooling that's Dirt Cheap! www.pinksdx.com |
|
|
senecarr
 Basic Member
 Posts:211
 |
| 19 Feb 2009 12:34 PM |
|
Isn't it possible to chain them in series? Considering radiant heating rather a luxury way of heating that gets lower performance, I don't see why you need tax relief on it. |
|
|
|
|
hector8762
 New Member
 Posts:23
 |
| 19 Feb 2009 12:36 PM |
|
Paul,
I've got a full SIP shell. R-38 in the ceiling and R-26 in the walls. No blower door test yet, but I've made every attempt to seal it up tight. I took advantage of passive solar design to the extent my lot allows. Now, I certainly could have built a smaller house. But, for the sq ft, my heating and cooling loads are very modest... Just over 5 ton of heating and 3.5 ton of cooling for a 4500 sf house in the mid-atlantic is not bad. Other than cutting the house in half, I don't know how I'd get those numbers much lower.
Tech,
Energy Star sounds like a great idea, but the execution is sorely lacking. For instance, ES requirements for your basic ground loop GSHP are 14.1 SEER and 3.3 COP. My choice of twin heat pumps would perform at 18 SEER and 3.4 COP. In terms of the stated goals of the tax credit, that SHOULD qualify. But it doesn't. Why? Because the rules are written to be easily enforceable, not to make any kind of sense. If a person acheives the stated performance goals, they should receive the credit.
Because the rules are written with so little thought, I'm going to have to buy a piece of equipment that's more complex and expensive than I require. I'm also going to end up with a heat pump that's undersized on the heat side, forcing me to suppliment with a far less efficient source.
Or, alternatively, I could scrap my efficient radiant floors and use 20% more energy to heat my house with forced air, using an 8-ton Energy Star rated heat pump.
In other words, I have to WASTE resources in order to qualify for a resource conservation incentive. You're going to have a tough time convincing me that makes any kind of sense.
Tuff,
I know. But it's hard not to hope for something better.
Seneca,
Probably possible to chain together multiple hp's. But, again, it's hard to see how that serves any useful purpose.
As far as radiant heat, I don't see it as that much of a luxury. I'm tired of paying $300/month to heat my Ryland townhouse (In which, by the way, I paid extra to get the Energy Star package) and still have to stand on ice cold floors. There's certainly an overhead cost to the distribution system. But I think the value from that investment is much better than, say, $12k worth of marble countertops. It's also, by all accounts I've found, more efficient than forced air. That should be in concert with the conservation goals of the current tax credits.
I suppose it also depends on motive. If the intent of the legislation is to promote conservation and lessen the amount of fuel used and emmisions created, then it makes sense to reward all of those who acheive those goals by the target amount.
On the other hand, if it's a need-based subsidy, then don't pretend to care about energy conservation or pollution. The earth doesn't care about the income of the family that creates the emmisions. Future generations that pay $5/KWH won't care about the income of the generations that squandered all the resources. |
|
|
|
|
joe.ami
 Veteran Member
 Posts:1653
 |
| 19 Feb 2009 11:24 PM |
|
i'm sorry, are you suggesting that radiant floors are more efficient than forced air? |
|
Just a Mechanic; Geothermal; Savings Underfoot |
|
|
cnygeo
 Basic Member
 Posts:139
 |
| 20 Feb 2009 12:19 AM |
|
Posted By joe.ami on 02/19/2009 11:24 PM i'm sorry, are you suggesting that radiant floors are more efficient than forced air?
Joe, I know we had a lively discussion on this issue a while back, so I'll just maintain that radiant floors CAN be as efficient or more so than forced air, even if they aren't usually. If I was designing the ultimately efficient system and money was no object I'd use radiant.
Unfortunately it seems not to matter how efficient a radiant system is since to be energy star qualified the unit must be rated under ISO whatever-1 which is a forced air test. Water-water heat pumps are rated under ISO whatever-2 so it seems to me that even if the COP was 10 they still could not be energy star rated due to what I consider to be a technicality.
|
|
|
|
|
joe.ami
 Veteran Member
 Posts:1653
 |
| 20 Feb 2009 08:05 AM |
|
For the purposes of this thread, I would install a water to air system for heating and cooling (instead of water to water with an air handler) and use the water to water floors for my auxiliary heat nice and energy star qualified, can also share loop field and is all tax credit worthy (whether or not water to water is ES rated, it is the back-up coil). As far as why you should have to pay extra, every body does that wants to qualify for the tax credit. There are water to air GTpumps out there that aren't ES rated (that cost less). Further, nobody installs in floor heat to save money it's a preference, comfy I'll grant you, but a luxury item. CNY- lively's often what I do around here:) J |
|
Just a Mechanic; Geothermal; Savings Underfoot |
|
|
hector8762
 New Member
 Posts:23
 |
| 20 Feb 2009 08:22 AM |
|
Joe,
I'm not a building science specialist. But I am an engineer that's spent the past 12 years researching residential building technology. In that research, I have found a large volume of material that suggests radiant floors are an efficient way to deliver heat. Given that there's an entire forum here at GreenBuildingTALK that's devoted to radiant heating, it appears that I'm not the only one who's drawn that conclusion.
That's not to say that I've considered every variable, or that my conclusion is unquestionably correct. But, the reasons given to support radiant floors and thermal mass make sense to me. I believe that I've chosen a system that is efficient for my application. Maybe you know better than I do. Maybe you don't.
The real point I'm trying to make here is that none of this is considered in this conservation incentive. The Energy Star folks don't give a damn if I blow 120,000 btu's past fiberglass insulation and leaky windows. As long as I generate all those btu's at a COP of 3.3 or better, I'd get my 30% back.
But if I cut my energy usage in half - which SHOULD be the ultimate goal here - and deliver the heat through the floors, that doesn't qualify. That makes no sense to me.
Jon
|
|
|
|
|
joe.ami
 Veteran Member
 Posts:1653
 |
| 20 Feb 2009 09:14 AM |
|
Ok...if we don't debate the floors or the tax law,
I still suggest a 3.5 ton water to air unit as your "primary" system, with a 5 ton water to water "back-up". Yes this will cost a few grand more than an air handler and water coil, but it will have a higher EER serve as an excellant back-up system and likely qualify for the tax credit. Joe
|
|
Just a Mechanic; Geothermal; Savings Underfoot |
|
|
hector8762
 New Member
 Posts:23
 |
| 20 Feb 2009 10:01 AM |
|
I don't know how likely that system would be to qualify. We're all guessing at the particulars here. My guess is that the 3.5 ton system would qualify, but the 5 ton system would not.
I've never considered a single w2w with an air handler. My cooling/heating loads don't support it. Geo pumps are biased towards cooling, my loads are biased towards heating. I've got to have dual systems.
The path I'm traveling down is not all that different than the one you've suggested. I'm having an 18-SEER air-source heat pump installed. That will provide the efficient AC, as well as fast-response heat during the shoulder seasons. The downside to this choice is that it won't provide supplemental heat when I need it most - ie when it's 5 degrees outside. Your system would excel there, but at a substantial additional cost.
To provide the heat, I'll need a 6 ton Synergy3D. That's not the best choice, for a variety of reasons. But it's the only choice that's government approved. When it gets really cold outside, I'll have to fire up the masonry heater.
I wish I knew more about the field-sharing you mentioned. I've considered this possibility, but never found any information about it. I might have gone with dual geo pumps if I was confident in the installation details.
|
|
|
|
|
joe.ami
 Veteran Member
 Posts:1653
 |
| 20 Feb 2009 10:17 AM |
|
Two things come to mind 1) as you pointed out 6 tons is not ideal but you could use it with a hydronic fan coil for cooling (you could use a 3.5 ton water coil and buffer tank for better dehumidification) that would likely be less expensive than the 18 seer ASHP. Throw in an electric aux coil and you have your back-up. 2) I've never been required to break down cost of geo vs ducts or aux heat etc. for a homeowner before, but of course the ink is hardly dry on the last tax credit let alone this one. Loop sharing in your case, I'd probably go with a 7 ton field a 5 ton water to water and a 2 stage water to air if I wanted to use geo/air as back up or you could use a 5 ton loop system and electric coil aux. if you didn't have space or means for extra ton. There are other ways (ie electric or gas water heater back-up) but there's some ideas. J |
|
Just a Mechanic; Geothermal; Savings Underfoot |
|
|
joe.ami
 Veteran Member
 Posts:1653
 |
| 20 Feb 2009 10:21 AM |
|
Should mention I shorted the loop requirement for the water to air unit, so you would only be able to use 1st stage heating. Many less RPM's will keep it from being too noticable. J |
|
Just a Mechanic; Geothermal; Savings Underfoot |
|
|
joe.ami
 Veteran Member
 Posts:1653
 |
| 20 Feb 2009 10:21 AM |
|
Should mention I shorted the loop requirement for the water to air unit, so you would only be able to use 1st stage heating. Many less RPM's will keep it from being too noticable. J |
|
Just a Mechanic; Geothermal; Savings Underfoot |
|
|
tuffluckdriller
 Advanced Member
 Posts:610

 |
| 20 Feb 2009 11:28 AM |
|
Just thought I'd mention in answer to the first post...
EarthLinked's DX heat pump will heat the water for your radiant floor, heat and cool air, and heat domestic water. It definitely is energy star rated and would therefore comply with the requirement for the tax credit. So it's not just the waterfurnace Synergy3d that's available. |
|
Clark Timothy (clark@pinksdx.com) VP sales, Tuff Luck Geothermal Drilling Geothermal Heat Pumps: Heating and Cooling that's Dirt Cheap! www.pinksdx.com |
|
|
hector8762
 New Member
 Posts:23
 |
| 20 Feb 2009 12:50 PM |
|
Joe, I appreciate the suggestions. I'll crunch some numbers and see it I can work it out.
Clark,
Do you have any product information for the Earthlinked DX pumps? I've been trying to find a product spec sheet, but haven't had any luck. |
|
|
|
|
bartman99
 New Member
 Posts:51
 |
| 20 Feb 2009 01:15 PM |
|
Well I am in a similar situation. I am upgrading our current heating and cooling system with Geothermal. Unfortunatley (for tax purposes) our current setup is all hydronic. I have hydronic RFH heated with propane and an ineffiecnt air-->water chiller supplying chilled water to air handlers for AC. The GTHP was going to replace thse two systems. Not that I was planning on the tax credit when I signed up for the geothermal HP upgrade, but it sure would have been nice!
I guess we can't really blame the IRS or the lawmakers for this. I think they needed something to use as a basis for effieicney and Energy Star seems to fit the bill. Perhaps the powers that be at ES need to be a little more open minded about ways of accessing the energy efficiency of well established technology (W-->W HP's).
BM
|
|
|
|
|
dmaceld
 Advanced Member
 Posts:860
 |
| 20 Feb 2009 11:06 PM |
|
Are you building on slab or over a crawlspace? Or are you building yet? If over a crawl space consider doing what I did, use the crawl space as the supply plenum. I built with ICF with sealed and conditioned crawl and attic. I have the heat pump air handler in the crawl space and dump the air out of short ducts into the crawl. It comes up through registers scattered around the perimeter just like a conventional FHA system. With the HP running the floor temp is about 2 to 4° above the living space air temp. This gives me a quasi radiant heated floor at the price of forced air.
|
|
| Building house - what a way to spend retirement! It's done! We're living in it! |
|
|
tuffluckdriller
 Advanced Member
 Posts:610

 |
| 20 Feb 2009 11:23 PM |
|
dmaceld,
Did you insulate the floor in that crawl? How are your bills? How is the comfort? Does it distribute evenly enough? And do you use any cooling? |
|