Posted By pp270 on 06/09/2009 12:24 PM
Especially the extra features it offers that the competition doesn't like the patented water heating system, redundent compressors and the ease to monitor system performance.
This is where it sounds like a sales pitch.^^^
The only hickup we have had so far is a low pressure warning is flagged everytime our in floor heat for the garage turns on. So far the explanation we have been given for this is the in coming antifreeze temp from the garage to the heat pump is to low thus tripping the error. This error never shuts down the unit, but does require it to reset several times. Every time it resets the in coming liquid is warmed slightly where eventually the systems continues to run. I am concerned the additional cycling of the compressors will reduce their long term life.
To answer your question short cycling can have an effect on system life , how much so depends on how frequently it happens , and how short the cycle .
I would assume there is no buffer tank , or its way to small , because otherwise you would not be having this problem .
You could also keep the floor a few degrees warmer to prevent the low pressure trip
You also could decrease the gpm going to the garage , eff. wise this would be last resort