snowaway3User is Offline
New Member
New Member
Send Private Message
Posts:5

--
30 Mar 2009 09:48 AM
i plan on installing a climatemaster tt27 5 ton unit. i live in ohio with heavy wet clay soil. plan on using 3/4' pipe for loop field with a header using 1.25" 100ft. who much total loop sounds right to use. have a guy stating 4000" and another says 2600" is fine.  I thought 400-600. per ton was what u usually use. this is a hor. loop 7ft. deep.
joe.amiUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1661

--
30 Mar 2009 10:43 AM
I don't know where u are at in OH. So don't know if I can compare to mid MI.
Much depends on wether they are using 1, 2, 4, 6 pipe or slinkies.
Proximity between trenches and wether your soil is really wet or just damp all have impact as well.
j
Just a Mechanic;
Geothermal; Savings Underfoot
zeyUser is Offline
New Member
New Member
Send Private Message
Posts:4

--
30 Mar 2009 10:05 PM
our site conditions in upper michigan. trench: 8' wide, 300' long and 6' deep. sandy some gravel soil with a water table between 3 and 4'. 4 ton econar geosource vara 2 plus unit. 4 - 3/4" pipes out circled back : 1' space between pipes. 1.25" manifold
zaraUser is Offline
New Member
New Member
Send Private Message
Posts:3

--
30 Mar 2009 11:00 PM
Horrible situation. I was excavating my bathroom floor and broke one of the plastic tubes that are part of the floor heating system. Does anyone know how I can mend it? It started leaking and I turned off the water main, but there are a couple of holes in it. Is there a repair kit for the tubing, could it be mended with copper fittings? Any help would be greatly appreciated! Zara



heimdmUser is Offline
New Member
New Member
Send Private Message
Posts:56

--
30 Mar 2009 11:34 PM

We are getting our tranquility 27 (064) 5 ton unit installed next week. We have very wet clay soil. I am located 1/2 between bloomington, IN and Indianapolis. The design for for 2in pipes to the mainifold. At that point, it breaks into 2, 300ft loops. They are using 6 pipe with 4 of them burried at 6ft and 2 at 3ft.

Our installer said that based on the soil we have we could probably get away with 200ft loops. We decided to go with the bigger loop. Our loop field is actually being run through the forrest next to our house.

joe.amiUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1661

--
31 Mar 2009 09:07 AM
Ok, so you are not using 4000 feet of loops (3600 is closer). 150' of trench/ton/6 pipe is common in mid MI and real overkill there. Wont hurt anything but is not automatically a good thing (more pump wear, more exposure to damage, more expensive to install). What configuration was your other bidder using (slinkies, 6 pipe)? I have to wonder if your installer has any product confidence his 200' of loops is just shy of the other guy's.
Based soley on the information before me I would have to guess that (again if we're talking 6 pipe) the installer you didn't hire is more expert than the one who throws pipe at a project just 'cause.
j
Just a Mechanic;
Geothermal; Savings Underfoot
heimdmUser is Offline
New Member
New Member
Send Private Message
Posts:56

--
31 Mar 2009 09:12 AM
In my case, the local water furance dealer who has the geo accreditation, said just to do vertical wells, this is the same one who didn't do an official heat and cooling load.
You are not authorized to post a reply.

Active Forums 4.1
Membership Membership: Latest New User Latest: Mahoney91 New Today New Today: 3 New Yesterday New Yesterday: 10 User Count Overall: 17378
People Online People Online: Visitors Visitors: 322 Members Members: 16 Total Total: 338

GreenBuildingTalk

Welcome to GreenBuildingTalk, the largest, most active forum on green building. While you can browse the site as a guest, you need to register in order to post.

Register Member Login Forum Home

Search Directory

Professionals Products

Get Free Quotes

Tell us about your building project and get free quotes from green building professionals. It's fast & easy! Click here to get your free quote.

Site Sponsors

For Advertising Info:
Call 866-316-5300 or 312-223-1600

Professionals Serving Your Area:

Copyright 2010 by BuildCentral, Inc.   Terms Of Use  Privacy Statement  Free Quotes  Professional Directory  Advertising Programs