I'm building a new home in west central Indiana. My home is stick built, 2500 sqft single story, and full (partially finished) basement (10 inch poured walls) totally underground, total 5000 sqft. Blown cellulose insulation, R38 ceiling, R15 walls. Pella Low E argon filled windows, and full brick exterior.
I've gotten two quotes for a geothermal system, but both estimate very different heating and cooling needs.
quote #1,
3 ton horizontal closed loop,
two stage compressor,
variable speed blower fan,
electric backup heat,
heat 3.59 COP,
cool 15.6 EER,
60,000 Btu/hr heating load,
33,000 Btu/hr cooling load,
heat,cool,hot water-$644+$115+$217 = $976 annual,
average monthly cost $81,
quote #2,
4 ton horizontal closed loop,
two stage compressor,
electric backup heat,
heat 3.35 COP,
cool 16.91 EER,
91,000 Btu/hr heating load,
47,000 Btu/hr cooling load,
heat,cool,hot water-$1126+$209+$288 = $1623 annual,
average monthly cost $135,
The initial total costs of the systems are pretty close. However, the anticipated operation costs are considerably different. Obviously, quote #1 looks the best with it's lower operation costs, but is the 3 ton system large enough? Please help with comments and suggestions, Thanks. |