Our mechanical engineer just recommended a fhp ww072 6 ton heat pump (water to water) for our radiant heating a single story 3000sqft new house. Wondering if anyone has any experience with this heat pump?
|
|
|
|
|
|
|
geotek
 Basic Member
 Posts:154
 |
| 12 Mar 2010 05:53 PM |
|
A proper installation done by an experienced installer is more important than a brand name. Choose your installer carefully and ask about warranty details.
|
|
|
|
|
engineer
 Veteran Member
 Posts:2749
 |
| 12 Mar 2010 07:37 PM |
|
Did your mech E perform a load calculation in compliance with ACCA manuals J and S before making that recommendation? Ask him or her why FHP over Water Furnace or Climate Master. I second the statement that the quality of the design and installation trumps brand issues
|
|
Curt Kinder <br><br>
The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
|
|
|
emjohnso
 New Member
 Posts:5
 |
| 13 Mar 2010 12:53 AM |
|
Will ask the questions and get all the load calc's/heat loss stuff early next week. Wondering what are the differences between the various brands, Water Furnace/Climate Master, etc.....
|
|
|
|
|
geotek
 Basic Member
 Posts:154
 |
| 13 Mar 2010 07:55 AM |
|
Differences are minor. Warranties can vary (your installer plays a part in the warranty). Two stage compressor can improve efficiency since loads are a moving target (referring to seasons).
|
|
|
|
|
geome
 Advanced Member
 Posts:987
 |
| 13 Mar 2010 08:45 AM |
|
The manufacturers web sites have manuals posted on their units. You can take a look to see the differences in features and efficiency. |
|
| Homeowner with WF Envision NDV038 (packaged) & NDZ026 (split), one 3000' 4 pipe closed horizontal ground loop, Prestige thermostats, desuperheaters, 85 gal. Marathon. |
|
|
engineer
 Veteran Member
 Posts:2749
 |
| 13 Mar 2010 11:55 AM |
|
Nearly all the two stage high-end units use Copeland 2 stage Ultratech compressors and similar peripherals so brand-to-brand differences are generally minor A heating-only radiant system with a reasonably decent sized buffer tank may benefit less or none at all from a 2 stage unit. |
|
Curt Kinder <br><br>
The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
|
|
|
geotek
 Basic Member
 Posts:154
 |
| 15 Mar 2010 10:08 AM |
|
A heating-only radiant system with a reasonably decent sized buffer tank
may benefit less or none at all from a 2 stage unit.
Agreed - but with GEO W to W one should take advantage of cooling use also.
|
|
|
|
|
joe.ami
 Veteran Member
 Posts:4377

 |
| 15 Mar 2010 10:27 AM |
|
Posted By geotek on 15 Mar 2010 10:08 AM A heating-only radiant system with a reasonably decent sized buffer tank may benefit less or none at all from a 2 stage unit.
Agreed - but with GEO W to W one should take advantage of cooling use also.
If cooling with hydronic fan coils, buffer tank is still employed and 2 stage unit may still not have big advantage. j |
|
Joe Hardin www.amicontracting.com We Dig Comfort! www.doityourselfgeothermal.com Dig Your Own Comfort! |
|
|
emjohnso
 New Member
 Posts:5
 |
| 15 Mar 2010 12:07 PM |
|
Thanks for all the information. I will have a meeting hopefully this week to find out the details of the recommendation. I'm sure this is a heating only location, jackson,WY, I know he was looking at the largest single stage pumps and came up with the 6 ton fhp, then mentioned he found a 10 ton. These seem pretty large to me, and said the cost is only 6K and 11K, that seems low to me with all the mentions on this site being in 25K+ range for smaller systems. More later.
|
|
|
|
|
emjohnso
 New Member
 Posts:5
 |
| 18 Mar 2010 07:35 PM |
|
Meeting is next week, but I did find out he wants to use a 10 ton unit now and 30 gpm instead of the 6 ton at 14 gpm. Basic difference is I want to put the pex tubing in my garage so I can melt the snow off the cars in the winter but basically keep the temps around 40 in the garage. Well water temps are cold, some say 41-42 degrees, others say 47-48 degrees, how much does that matter. Either of these units seem large, with the 10 ton being way over the top to me. I'm putting in R40 walls and R60-70 roof insulation so the envelope should be good. They think there should be adequate heat. Will get the raw numbers next week. Just want a ballpark are these units large? and will they last? or require maintenance due to water quality issues.
|
|
|
|
|
engineer
 Veteran Member
 Posts:2749
 |
| 18 Mar 2010 09:54 PM |
|
Yes X 3. |
|
Curt Kinder <br><br>
The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
|
|
|
joe.ami
 Veteran Member
 Posts:4377

 |
| 22 Mar 2010 08:20 AM |
|
Once you have a heat loss calc, we will be able to answer your questions about size. Regarding price, there is a big difference between off the rack and installed pricing. There is also a big difference between the cost of open and closed loop installation cost (could be more than $10,000 on a 10 ton). j |
|
Joe Hardin www.amicontracting.com We Dig Comfort! www.doityourselfgeothermal.com Dig Your Own Comfort! |
|
|
emjohnso
 New Member
 Posts:5
 |
| 24 Mar 2010 10:47 AM |
|
Heat Loss was calculated at 105,000BTu/hr and the 6 or 10 ton unit, with lots of supplemental heat in various rooms. We get days/weeks of minus 0 temps, so the effectiveness of geothermal in my opinion is limited. The payback period was at least 11 years, so we decided to go with a electric boiler and put more money in the envelope than the system heating it.
|
|
|
|
|
joe.ami
 Veteran Member
 Posts:4377

 |
| 24 Mar 2010 10:27 PM |
|
in my area 105kbtu would suggest ~6 tons. When you say pay back was at least 11 years that is assuming anything else you install owes you nothing. Everything else is a loser and geo ECLIPSES them in ~11 years. Problem here is your designer doesn't seem to know geo either. J |
|
Joe Hardin www.amicontracting.com We Dig Comfort! www.doityourselfgeothermal.com Dig Your Own Comfort! |
|
|