Open loop Geo system not cooling as normal
Last Post 17 May 2015 10:13 AM by joe.ami. 30 Replies.
lawtoolguyUser is Offline
25 Dec 2014 01:14 PM
Posted By joe.ami on 25 Dec 2014 08:24 AM
What are the pressures supposed to be?
When first fired up Low Side was 60 psi and high side 195 psi. Worked fine for first 3 years with 22 degree temp difference from supply and return
25 Dec 2014 01:46 PM
Posted By jonr on 25 Dec 2014 11:23 AM
You could take a small sample of the HX deposits and test various acids against it in a glass. Take the best and use it liberally (you have little to lose at this point).
I haven't looked into it, but perhaps sulfamic or hydrochloric, both with an inhibitor.
I've got a few months to decide but so far I haven't been able to find any replacement parts since it is a R-22 system. I'll drain HX again and try to get a good sample to test. Thanks for the help
27 Dec 2014 07:24 AM
"Return air 80* Supply air 73* low side 67 psi high side 230 psi suction 75* Liquid 95* 5 GPM 75* EWT 87* LWT......."
"Low Side was 60 psi and high side 195 psi. Worked fine for first 3 years with 22 degree temp difference from supply and return"
Numbers mean more when you have all of them. Things that run pressures up include air and water temps which you didn't provide for your base line numbers.
I missed this before but are you really only getting a 7F drop in air temp while cooling?
27 Dec 2014 09:26 AM
Flushed with solution of sulfamic acid for 1 day
With poor results
After flush
Low side 60
High side 225
WX in 21 psi
WX out 18 psi
5 GPM
Supply 68
Return 72
Suction 70
Liquid 88
EWT TEMP 75
LWT 84
Outside temp now 62 but is supposed to warm up today
To 78
27 Dec 2014 12:06 PM
Not my area, but are your results consistent with a worn out compressor that isn't producing much flow (with the TXV maintaining the pressure)?
29 Dec 2014 09:37 AM
The results are consistent with a dirty HX (fan coil or coax)
29 Dec 2014 11:15 AM
Posted By jonr on 27 Dec 2014 12:06 PM
Not my area, but are your results consistent with a worn out compressor that isn't producing much flow?
Compressor is fine no noise or power draw. Unfortunately I'm going to have to either have system Drained again and remove WX and maybe have it ultrasonic Cleaned or give up and buy a 4 ton R-22 condenser. I am going to try to call Tetco today to see if they still Supply these WX other wise I'm spinning wheels.
30 Dec 2014 10:27 AM
Second opinion is worthwhile before jerking heat ex.
30 Dec 2014 10:58 AM
Posted By joe.ami on 30 Dec 2014 10:27 AM
Hey Joe Would be a third opinion as my A/C guy has been Saying all along that it acts like condenser is dirty (waterside exchanger). I think the TXV was bad from factory as I installed this unit In another house I built in PA but would not heat always Ran toaster. Unit was sent prematurely before I ordered It. Called company and they were out of business. Replaced it with a water furnace and had no issues. Heated and cooled great with same closed loop system. I'm guessing the TXV was bad from get go but seized open enough for cooling cycle To work fine for 3 years until HX started to foul and cause my Original high side trips this past summer. After replacing TXV That corrected metering and got my pressured back to a except able level and stopped my high side trips but still no where near efficient. At this point its more of a project since temps are perfect and we haven't used the heat since we moved in 3 years ago.
16 May 2015 06:26 PM
We decided to move on. Replacing WS ex changer seemed like throwing good money away on 22 system. I bought a new 3 ton Rudd 410 system and completed install today. After pumping system down below 500 micron I now know how long it takes to do a true vacumm. Took almost two hours with a brand new JB eliminater at 6 CFM.
Thanks for the help!
Hope all goes well for you.
Membership Membership: Latest New User Latest: Coconut Canadian New Today New Today: 0 New Yesterday New Yesterday: 0 User Count Overall: 34736
People Online People Online: Visitors Visitors: 282 Members Members: 0 Total Total: 282