Problem with Water furnace ND038
Last Post 29 Jul 2014 12:41 AM by docjenser. 26 Replies.
Printer Friendly
Sort:
PrevPrev NextNext
You are not authorized to post a reply.
Page 2 of 2 << < 12
Author Messages
joe.amiUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:4377
Avatar

--
27 Jul 2014 11:28 AM
Ok, slow down Bill. In trouble shooting you don't look for multiple problems at once. Something caused relays to fail and it may be as inocuous as cheap relays. New company used isolation valves to throttle pumps suggestiong (IMHO) ineptitude, then pump trouble started (where before only relays were failing). Then OP insisted on pump change whether we needed it or not....what a mess.

What you need to do is find out if you get enough GPM with one motor (simply disconnect power to one and watch temps). If you do great, if not then ask for correct pumps. Then find out why relays fail or do like half the free world and slave 1 pump to each compressor contactor.

High loop temp didn't show up until some bozo throttled the loop pumps. Don't assume trouble with ground loops until we get a handle on flow....
and don't believe temps from an infrared source.


Joe Hardin
www.amicontracting.com
We Dig Comfort!
www.doityourselfgeothermal.com
Dig Your Own Comfort!
Bill NeukranzUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1103

--
27 Jul 2014 01:12 PM
Posted By joe.ami on 27 Jul 2014 11:28 AM

Ok, slow down Bill.
 
In trouble shooting you don't look for multiple problems at once. Something caused relays to fail and it may be as inocuous as cheap relays.
 
New company used isolation valves to throttle pumps ... , then pump trouble started (where before only relays were failing).
 
Then OP insisted on pump change whether we needed it or not....  ....

What you need to do is find out if you get enough GPM with one motor (simply disconnect power to one and watch temps). If you do great, if not then ask for correct pumps.
 
Then find out why relays fail ...

High loop temp didn't show up until ... throttled ... loop pumps. Don't assume trouble with ground loops until we get a handle on flow....
 
and don't believe temps from an infrared source.

!!!

Best regards,

Bill


Energy reduction & monitoring</br>
American Energy Efficiencies, Inc - Dallas, TX <A
href="http://www.americaneei.com">
(www.americaneei.com)</A></br>
Example monitoring system: <A href="http://www.welserver.com/WEL0043"> www.welserver.com/WEL0043</A>
MFRichardsonUser is Offline
New Member
New Member
Send Private Message
Posts:10

--
27 Jul 2014 02:55 PM
3:00 PM update
97 outside
74 inside
Water in 101
Water out 105
Both pumps 142


MFRichardsonUser is Offline
New Member
New Member
Send Private Message
Posts:10

--
27 Jul 2014 03:41 PM
Additional update
I disconnected the bottom pump
Everything still working
Top pump varies from 129 to 134
Room with A/C Units 92
Summary disconnecting the bottom pump has caused a reduction of approximately 10 degrees in the top pump
I am measuring with a Brand new and calibrated Flir E5. the motor temperatures are accurate. Measuring the water temperature inside a pipe is not. I am measuring the brass fittings on the ground loop that are affected by the ambient temperature
also the A/C units are cycling on / off that affects the water temperature
Can someone explain how turning off one pump reduces the motor temperature?


joe.amiUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:4377
Avatar

--
28 Jul 2014 11:02 AM
Hot pumps are contributing to the water temp.
Was my last suggestion so disinteresting as to be completely ignored?


Joe Hardin
www.amicontracting.com
We Dig Comfort!
www.doityourselfgeothermal.com
Dig Your Own Comfort!
joe.amiUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:4377
Avatar

--
28 Jul 2014 11:07 AM
......I mean we get that loop temps and pumps are hot, but you are directing the focus just as you directed replacement of pumps whether they needed it or not.
Good Luck.


Joe Hardin
www.amicontracting.com
We Dig Comfort!
www.doityourselfgeothermal.com
Dig Your Own Comfort!
docjenserUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1400

--
29 Jul 2014 12:41 AM
open them full. geo is all about flow. Let it flow....


www.buffalogeothermalheating.com