OK, after going through a WEL (monitoring system) repair cycle (electrical surge), WEL0043 is back up and running (
http://www.welserver.com/WEL0043/ ).
You may recall that last month I disconnected one of the 2 pumps for my WaterFurnace geo-HVAC 5 ton unit, prompted by many here, as an experiment to learn from.
I continue to run my 5 ton unit with just one loop pump (the 'pulling' portion of the push-pull configuration). And it continues to work fine. I marvel at how a non-functioning pump can still be left in the loop circuit without significant performance impact (or that the loop is even runs at all - the non-functioning pumps propeller must be simply doing a 'free-spin,' versus causing a blockage.)
Running a 5.0 psi Pressure Differential (see earlier thread) through the WF Envision chart calculation yields 15.2 GPM at 77 degrees F. Down considerably from 21.2 gpm.
A key benefit of making this change is I'm running the 5 ton unit with about 385 Watts less of power.
I don't know if this is the 'bottom line,' or, if there are other benefits of running with less gpm through the coax heat exchanger. I.e., what about long term wear on the coax heat exchanger.
Just by using an 'eyeball' examination, it looks like EER improves a little, from approximately 20 to 21 BTU/W-hr. This makes sense.
Here's the whole picture for those interested (first number is with both pumps running, second number is with just one pump running):
Outside temp: 95 -> 95 degrees
EWT: 76.6 -> 76.0 degrees
DeltaT: 4.9 -> 7.1 degrees
Flow: 21.1 -> 15.2 GPM
Heat of Exchange: 52 -> 53 kBTU/hr
Compressor Discharge Line 121 -> 123 degrees
EAT: 78.5 -> 77.0 degrees
LAT: 58.0 -> 55.7 degrees
DeltaT: 20.5 -> 21.3 degrees
Air flow: CFM: 1500 -> 1500 CFM
Sub Cooling: 33 ->34 kBTU/hr
EER: 20 - 21 BTU/W-hr
(All of the above from my WEL unit)
This certainly is another lesson that simply cranking down flow with isolation valves does nothing to change performance.
BTW, this is all 1st stage only. I almost never have to run my unit in 2nd stage.
Hope this is interesting to those here.
I plan to leave the pump turned off.
Best regards,