I did try reversing the system the last time around when I was troubleshooting. Twice. Both time, the system went into LT2 lockout within minutes of startup.
An update to this recent round of troubleshooting. The system is still locking out, even with the DSH off, but not as frequently as it had been. What I have observed at the times of these lockouts is that they seem to coincide with large volumes of water usage, namely showers. What Bergey said was something I have been thinking for a while now and seems to fit:
Posted By Bergy on 12 Mar 2015 02:43 PM
ET,
Something in the system must be very marginal so when you "steal" a little heat from the compressor discharge line it tips the balance and locks out.
Bergy
Though even with the DSH off, when something like a shower happens I see water flowing through the DSH. My monitoring system shows the temperature drop on the DSH lines. As an example, the wife jumped in the shower and at 7:08 this morning I see the temperature of the DSH output line drop from 152F to 80F and the DSH input line from 89F to 53F. Coincidence? Maybe, but I don't buy that. If the flow of cold water into the DSH is enough of a drop to "Steal" enough heat from the system, maybe that is enough to trip LT1. If there are other factors like improper antifreeze leves, low refrigerant, etc, maybe those are the source of the problem, but my observations say that something having to do with the DSH is involved somehow. I have seen this behavior on multiple occasions when there is a large water draw. I have looked at the plumbing for the DSH and it appears to be correct according to the install instructions for a two-tank system. What I don't understand, since I don't know the internal mechanics and plumbing of the DSH pipes inside the unit, is why, when the DSH is disabled, does cold water continue to flow into and out of the system. Perhaps, with the DSH off, should I also close the valve that feeds cold water into the DSH to see if that makes any difference?
I know you all must think I am getting hung up on the DSH. I don't believe that it is the source of the problem, but I do believe that it exacerbates it somehow. I don't buy into coincidences. I believe in cause and effect. In the end, i really just want a working system that I don't have to babysit constantly and worry over whether or not it will lock out today, or tomorrow or next week. What I think makes things more difficult for me is that my installer, while trying to help resolve the issue, just doesn't seem to be very good at troubleshooting the problem, they take forever to call me back and they are more interested in their new installation jobs than they are in diagnosing and fixing broken systems. I am about ready to just cut bait with them and look for another service company. But since they installed the system, I have been reluctant to sever this relationship and I tend to try to give people the benefit of the doubt. I shouldn't have to spend hours trying to understand the nuances of heat pumps, refrigeration systems and desuperheater plumbing. Quite honestly, I have better things to do. But since I don't trust that my installer really has a handle on the problem, I come to forums like this to educate myself so that I know what should be done and whether they are feeding me a line of bullshit. At this point, they are scheduled to come out on Monday to replace the TXV. Everyone in the forum here has been quite helpful and I appreciate all the advice. Here's to hoping things get resolved soon.