Posted By dolphin on 03 Mar 2010 03:14 PM
52722 is the Zip. I would like to make a decision... my mind is going to explode ;o) I am thinking of going with some sort of attic seal followed by blown fiberglass/cellulose on the attic floor to make up the differenct. Any suggestions would be greatly appreciated. Would a house plan help? Also, what do you think about the ceiling of the garage below the bonus room?
Bettendorf has about a 6500 heating degree-day climate with Dec/Jan/Feb average temps of ~25F/20F/25F respectively. (Climate info for the quad-cities lives
here.) You definitely need more than ~R20 (5-6" of half-pound foam) in the attic to keep heating bills bounded. The Oak Ridge Nat'l Labs zip code recommendations for your zip calls for R49 in the attic, but you can safely split it between foamed rafters & fiber-insulated floor if you follow this rough guideline:
Don't go more than ~R40 on the floor portion- not the full R49. Keep the fiber to 2/3 of the total R-value or less, or you run a risk of wintertime condensation/mildew issues in the attic. Monitor the relative humidity in the attic during the first winter season- if it stays at 70% or higher for weeks on end, put a dehumidifier up there to keep it at 60% or less. The duty cycle will be low- the heating savings will more than offset a few kwh/month in dehumidification costs.
But if you seal it well at the ceiling below you probably won't need mechanical dehumidifation if you keep it to 1/3-2/3 in your location. The less warm air from conditioned space infiltrates into the now-sealed attic, the lower the humidity issue. Foam sealing all plumbing & electrical penetrations into that area is best. If you have a bunch of recessed lights it's a real PITA though. Blown cellulose passes significantly less air than batts or blown fiberglass, and will wick any condensation that DOES occur away from structural materials. This hygric buffering effect makes the attic more moisture-tolerant and moderates the humidity. (The only down side to insulating attics with cellulose is when roof leaks occur it doesn't dry quickly, and it's better to scoop out any wet stuff and replace it with fresh stuff. ) Use weather stripping or other air-sealing methods on the attic access as well. Applying vapor-retardent paints on the ceilings below the attic floor is also a good idea, but not nearly as important as air-sealing. Air transported moisture will usually greater than vapor-diffusion through wall surfaces. If you use cellulose to buffer it and reasonable air sealing you'll be in good shape. During the spring/summer/fall the cellulose will dry sufficiently to buffer the following heating season's humidity load.
If you already have R49 batts up there, leave them, but plan on monitoring the RH and dehumidifying as-necessary. The risk is low, but not as low as if you had less air-permeable insulation and more hygric buffer.
Under the bonus room applying a 2" lift of 2lb (closed cell) foam on the sub-floor from below both air seals it an puts a class-II vapor retarder on the correct (warmer in winter) side of the assembly. Rather than batts, again blown insulation is your friend, as it leaves no gaps. With a warm-side up configuration with a perfect air seal (the foam) there's less convection loss (= performance reduction) that you'd otherwise get with fiberglass, but blown fiberglass is far preferable to batts. Cellulose weighs more, but may be preferable here too (again, for hygric buffering reasons, though it's less critical here.)