Insulating an old stone basement
Last Post 22 Jun 2012 06:11 PM by Dana1. 1 Replies.
Printer Friendly
Sort:
PrevPrev NextNext
You are not authorized to post a reply.
Author Messages
geekUser is Offline
New Member
New Member
Send Private Message
Posts:11

--
22 Jun 2012 05:04 PM
Do I really need a capillary break between my foundation and my sill if I sprayfoam the interior of my foundation to insulate the basement or are there any alternatives? 

It is a 90 year old stone foundation with 9-12 inches above grade on the exterior (at the moment).  80% of the basement is a full basement and 20% is a crawl space.   I would also like to put a moisture barrier down in the crawl space, FYI.

Dana1User is Offline
Senior Member
Senior Member
Send Private Message
Posts:6991

--
22 Jun 2012 06:11 PM
Stone is not concrete- most stone used in foundations isn't nearly as porous as concrete. Furthermore most old stone has lots of air spaces, and drain pretty well, so there just isn't much capillary draw from the bottom subsoil on up to the top. There might be splash-back or bulk water issues causing rot to be dealt with first, but if it's under control that won't affect the insulation situation. Snow depth levels might though, if it commonly reaches the sill.

If it's 90 years old and there's no hint of rot on either the exterior or interior side, go for it. A 2" (or more) shot of closed cell foam works.

Stay away from open cell if there's even a hint of water seepage through the foundation anywhere. In colder climates with open cell it's possible to get wintertime moisture accumulation high enough for frost to form within the foam under certain conditions, which may impact long term adhesion, but not with closed cell.

Is there a slab/rat-slab, or is the basement floor dirt? Sometimes it's better to dig in a perimeter drain and put a continuous ground vapor retarder (and insulation, if it's cold climate) under a new slab as part of the whole renovation, making the the wall-insulation continuous with he floor insulation/vapor barrier. See some of the foundation wall & slab details in this retrofit:

https://www.powerofaction.com/media/pdf/DER_CaseStudy_Belchertown_MA.pdf

(Note that they did not insert a capillary break under the sill timber, and sprayed diretly onto the stone, no drainage mat, etc.)