Sandwitch wood in foam, bad idea?
Last Post 25 Oct 2009 09:11 AM by jonr. 18 Replies.
Printer Friendly
Sort:
PrevPrev NextNext
You are not authorized to post a reply.
Author Messages
aeridyneUser is Offline
New Member
New Member
Send Private Message
Posts:60

--
03 Sep 2009 02:57 PM
Standard Sips put the foam in the middle of two boards, so the wood can dry to either side in that scenario, I had a thought about design in my own home, but I didn't know if it was risky or not.

I'm guessing that there has to be someone who has done this before somewhere potentially by guidance to two different contractors and never even really thinking about it, anyway, here it is; what if you used rigid foam on both sides of osb? For example on an exterior wall, rigid foam on the exterior between the sheathing and siding, and also on the inside within the stud bays? Spray foam could have been used in the stud bays as well. I'm wondering how this would work? It seems like the wood in the center could potentially get wet and have no way to dry, but at the same time, it seems like someone must have done this before, and I've never heard of anyone having a problem with it either?

The way I was thinking of using it, was on an exterior wall, and in my roof, in both cases there would be 2" or more of xps on the exterior, and then I thought about using 1" in the stud/rafter bays, and sealing the edges with spray foam, but it seems like while this would create a really tight envelope, that it could create a moisture problem that I was trying to avoid in the first place.

thoughts? experiences? examples?

Thanks!
jdebreeUser is Offline
New Member
New Member
Send Private Message
Posts:40

--
03 Sep 2009 04:13 PM
You would lose almost all of the structural strength of a SIP. The strength comes from the two OSB panels being held rigidly X inches apart- it's almost as rigid as a solid piece. Putting a single layer of OSB between foam would be very flexible- you would have to have framing to support it. The idea of a structural SIP is that it is self-supporting- you don't need any framework (or very little).
toddmUser is Online
Basic Member
Basic Member
Send Private Message
Posts:252

--
03 Sep 2009 06:11 PM
If you are talking about standard stud wall construction with foam sheathing on the outside and spray foam or foam boards stuffed in the cavities, yes, it is eminently doable, and a fine answer for DIYers who have more time than money. A stick-built version of SIPs was my Plan B, in fact, buying reclaimed foam from these folks: http://www.insulationdepot.com/ You'd get a R30+, 2x6 wall for a very small premium. You'd use spray poIyurethane to fill in any gaps between foam pieces and studs.

I'd address water vapor issues by treating the wall as if the cavity insulation was all spray foam, which is done all the time. If you aer were pretty religious about fitting the foam pieces and sealing them, you'd get 80 to 90 percent of spray foam's tightness.

But none of its stuctural, adhesive properties, so if you have more money than time, spray foam is better.
aeridyneUser is Offline
New Member
New Member
Send Private Message
Posts:60

--
03 Sep 2009 08:20 PM
Posted By jdebree on 09/03/2009 4:13 PM
You would lose almost all of the structural strength of a SIP. The strength comes from the two OSB panels being held rigidly X inches apart- it's almost as rigid as a solid piece. Putting a single layer of OSB between foam would be very flexible- you would have to have framing to support it. The idea of a structural SIP is that it is self-supporting- you don't need any framework (or very little).

I was not intending on making structural sips, it will be a stick frame with osb sheathing, questions revolve around how to insulate that.
aeridyneUser is Offline
New Member
New Member
Send Private Message
Posts:60

--
03 Sep 2009 08:23 PM
Posted By toddm on 09/03/2009 6:11 PM
If you are talking about standard stud wall construction with foam sheathing on the outside and spray foam or foam boards stuffed in the cavities, yes, it is eminently doable, and a fine answer for DIYers who have more time than money. A stick-built version of SIPs was my Plan B, in fact, buying reclaimed foam from these folks: http://www.insulationdepot.com/ You'd get a R30+, 2x6 wall for a very small premium. You'd use spray poIyurethane to fill in any gaps between foam pieces and studs.

I'd address water vapor issues by treating the wall as if the cavity insulation was all spray foam, which is done all the time. If you aer were pretty religious about fitting the foam pieces and sealing them, you'd get 80 to 90 percent of spray foam's tightness.

But none of its stuctural, adhesive properties, so if you have more money than time, spray foam is better. [/quote]
Yes I am talking about standard stud wall construction, you are understanding that correct good sir. However, I'm not sure you caught what my conundrum is, if I used xps foam 2" or greater on the exterior of the sheathing, and then I did as you understood and described in the stud bays, that was the setting for my question. The osb will be in the middle of all of that sealed up tight foam, and that is precisely what I'm worried about.
JellyUser is Offline
Advanced Member
Advanced Member
Send Private Message
Posts:552

--
03 Sep 2009 09:37 PM
I think your instinct is correct, that it's a classic possible moisture problem. Just my opinion though.
toddmUser is Online
Basic Member
Basic Member
Send Private Message
Posts:252

--
04 Sep 2009 07:44 AM
Here is the spray foam industry's manual on vapor barriers http://www.sprayfoam.org/downloads/pdf/AY%20118.pdf

and Building Sciences take on vapor control in walls http://www.buildingscience.com/documents/reports/rr-0410-vapor-barriers-and-wall-design/view?topic=/resources/vapor_barrier_code_changes

The Cliff's Notes: Spray polyurethane and EPS are not vapor barriers, and XPS is considered semi impermeable only at an inch or more. You're a step ahead with the wall I described because there would be little or no air movement through it. How you deal with vapor pressure depends on where you are building.

Finally, you may not need OSB sheathing at all, except for the odd corner, depending on your building code.
aeridyneUser is Offline
New Member
New Member
Send Private Message
Posts:60

--
04 Sep 2009 11:28 AM
Posted By toddm on 09/04/2009 7:44 AM
Here is the spray foam industry's manual on vapor barriers http://www.sprayfoam.org/downloads/pdf/AY%20118.pdf

and Building Sciences take on vapor control in walls http://www.buildingscience.com/documents/reports/rr-0410-vapor-barriers-and-wall-design/view?topic=/resources/vapor_barrier_code_changes

The Cliff's Notes: Spray polyurethane and EPS are not vapor barriers, and XPS is considered semi impermeable only at an inch or more. You're a step ahead with the wall I described because there would be little or no air movement through it. How you deal with vapor pressure depends on where you are building.

Finally, you may not need OSB sheathing at all, except for the odd corner, depending on your building code.

So todd, you are saying that if I sealed it up real tight on both sides, I might not have a problem because it is thusly sealed?

I don't know, I'm apprehensive to do it that way, with 2" of xps on the outside it can only dry to the inside as it is, however the osb sheathing would be the only thing affected, I guess except for all the holes I'll probably punch in it when putting up the siding and attaching the 2" exterior foam as it is.

Perhaps I should just forget about it for the walls themselves, it might be a smarter thing to do, it just seemed to me that someone would have done this with XPS on the exterior and spray foam in the stud bays at some point, and wondered how it all worked out in the longrun, and further how it would work if the stud bays were to use the xps/seal w/ 1" spray foam technique and fill the rest w/ cellulose.

Pretty much all of my concerns revolve around making sure that cellulose never gets wet, in my roof assembly and my wall assemblies. And of the two, the roof is where I was thinking of using this method the most for a tighter seal.
toddmUser is Online
Basic Member
Basic Member
Send Private Message
Posts:252

--
04 Sep 2009 11:40 AM
Cudda been clearer I guess. No problemo in heating or cooling climates as long as you have the vapor barrier on the proper side and choose the right foam. In general you want the wall drying to the side with the least humidity, which translates to vapor barrier inside up north and outside down south. In the north, you'd want an inch or less of XPS as sheathing or any amount of EPS. In the south, more than an inch of XPS sheathing would sub for vapor barrier, but you'd need to add one over EPS sheathing (or use foil-faced boards.)
In the north XPS in the cavities could sub for a vapor barrier. Or add a barrier to EPS or polyurethane. Again, an XPS or foil backed EPS vapor barrier would be tighter than the kraft paper that does this work in walls with fiberglass batts. In the south you'd want EPS or polyurethane as cavity insulation.
Needless to say, we're talking about unfaced foam boards unless otherwise stated.
aeridyneUser is Offline
New Member
New Member
Send Private Message
Posts:60

--
04 Sep 2009 03:01 PM
**ok so apparently if you try to edit a post that has a quote, it's totally going to trap you in that box forever**

[quote]Posted By toddm on 09/04/2009 11:40 AM
Cudda been clearer I guess. No problemo in heating or cooling climates as long as you have the vapor barrier on the proper side and choose the right foam. In general you want the wall drying to the side with the least humidity, which translates to vapor barrier inside up north and outside down south. In the north, you'd want an inch or less of XPS as sheathing or any amount of EPS. In the south, more than an inch of XPS sheathing would sub for vapor barrier, but you'd need to add one over EPS sheathing (or use foil-faced boards.)
In the north XPS in the cavities could sub for a vapor barrier. Or add a barrier to EPS or polyurethane. Again, an XPS or foil backed EPS vapor barrier would be tighter than the kraft paper that does this work in walls with fiberglass batts. In the south you'd want EPS or polyurethane as cavity insulation.
Needless to say, we're talking about unfaced foam boards unless otherwise stated.
[/quote]

Perhaps I should be drinking more coffee... Btw, I live in Flint Mi, which is zone 5. I think it's between something like 6 to 8 thousand heating degree days.

Anyway, while I know you were trying to be clearer, actually I got a bit more confused. Regardless the effort is still appreciated of course.

It sounded like you were trying to say, that the exterior sheathing should be vapor permeable, and I should use only 1" of xps, or any depth of eps (because it is permeable) & I assume any non foil faced ISO would work too...

This is in conflict with what I have read on building sciences though?
http://www.airtightinsulation.com/UserFiles/File/building-science.pdf
(unless I'm reading that wrong too)

This is why I'm getting so confused, I read things on building science, I read things here and there and everywhere and they are all different, and I can't find but a scant few that point out how something was actually done, but not why, or specifically how things were done...

All of the assemblies I can find specific info on at building science and such use at least a 2" airspace, but I've heard many talk of no airspace at all, Dana on this forum for example said that airspace did little and was largely useless. I believe it was that person also who said you should at least observe a 1/3 2/3 rule of rigid R value on the exterior to the cavity R value on the interior. Now in the building science document there, they have more than one assembly similar to that, however, I don't really understand "potential for condensation" definitively other than taking it literally, but a roof that has that potential when it's 20 degrees outside and 70 inside @ 45% humidity is going to happen at some point and worse I'd wager...


I forgot to add, that I saw something on solar vapor drive, say the roof is wet, and then the sun comes out, wants to drive vapor inward into the roof assembly, key is to make sure it can't get in. I'm thinking about green roof design here, and as far as I know, they don't have any ventilation, just throw down a waterproof membrane and a bunch of other layers over foam and apparently that works? But do they fill in rafter bays with something I wonder...
toddmUser is Online
Basic Member
Basic Member
Send Private Message
Posts:252

--
04 Sep 2009 04:45 PM
I didn't know where you were until your last post, so you need to go with the person who has all the facts (you.) Also, I an strictly talking walls here. Roofs have the additional variable of vented vs unvented. But you now have Building Science's take on walls and roofs and you should be able to sort it out for yourself.

As for walls, EPS sheathing over fiberglass batts has been around for 30 years. Because EPS and spray foam are permeable, the only difference is the missing vapor barrier (provided by kraft paper on the batts.) Unless you use XPS. l
You are perhaps missing the fact that sealing a wall against air infiltration does not seal it against vapor pressure. Vapor moves from the warm side of the building envelope to cold side even in walls and roofs that are air tight. The point of a vapor barrier is to stop it with foil or polyethylene or something similarly impermeable before it gets into the envelope. You also want to provide an escape route on the other side through materials that are permeable.

Even then you aren't going to stop vapor, because the two sides of your walls and roof take turns being the warm side. So the trick is to look at your local climate and pick a side for the vapor barrier that will stop enough of the moisture to head off problems. That is simple in your case as finding Zone 5 in the Building Sciences pieces.

You don't say why you want XPS vs EPS or polyurethane. Personally, given the squishy nature of this question, I'd go with EPS sheathing. That said, I'll be stuffing XPS between the rafters in my unvented attic.
The SipperUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:231

--
04 Sep 2009 05:17 PM
aeridyne, is there any reason why you don't want to use SIPs for both your walls and roof? None of the complicated options that you're discussing, will give you a better result, nor will they cost less. There are volumes of information about SIPs on the interent, as well as on this website so I don't feel that a long winded "sales pitch" is in order. However, if you do have specific questions regarding this technology, I'd suggest that you post them down below on the "SIP Forum". Just a suggestion, good luck with your project, whatever you decide to do.
The Sipper
toddmUser is Online
Basic Member
Basic Member
Send Private Message
Posts:252

--
04 Sep 2009 05:53 PM
Beg to differ, Sipper. Insulation Depot is selling reclaimed 2" EPS for $6.67 a sheet (FOB Tennessee; truckload only.) Sheathing and stuffing 2x6 stud walls gets you R28 for about 83 cents a square foot. Studs are plenty cheap too.
The SipperUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:231

--
04 Sep 2009 06:26 PM
Differ all you want, I'll stand by the letter of my comments. However, I do agree with your statement that "studs are plenty cheap too".
The Sipper
mforgetUser is Offline
New Member
New Member
Send Private Message
Posts:5

--
05 Sep 2009 06:26 AM
i just finished building my house with 5in of stuffed EPS between 2x6 studs with PU sealing and an tyvek faced iso-cyanurate board laminated to the osb on the outside.

(SIPs require are suprisingly expensive in my area... about double the cost for my 1600sqft house)

the building engineer had no problem with the system and moisture because there was no air-space within the vapor-barrier layers for water to condense. (note: i also have a vapor barrier on the inside to block most of the interior vapor)

While this solution was quite easy and very low cost , i wont use the same system next time.

i plan on doing my next project with Dow SIS sheeting and dense-pack cellulose which should give me the same costs but be much quicker, less headache, and a lot lighter to handle.

the major issue with EPS is that it should really be installed WHILE the studs are assembled (vs stuffing the eps between the studs) but when you do so, you loose all nailing surfaces and can't fit the nailgun between the studs. (in my case, i was pre-building 4x8 panels)

i had greatly under-estimated the time required to measure and cut the EPS with a hot wire. (especially dealing with lumber warping and the amount of PU that ends up in your face when you push the EPS in ! ). no kidding... it was literally snowing PU inside the house.

not a bad system, but i suggest sis+3.5pcf cellulose ... less time, same R-value, same cost.

aeridyneUser is Offline
New Member
New Member
Send Private Message
Posts:60

--
08 Sep 2009 12:29 PM
Ok, I'll try to touch a bit on all those replies;

I am aware of vapor pressure, and yeah you'd think i might be able to extrapolate out of all those myriad documents and everything else I've been reading for months exactly what my best build would be, however, some of them seem to conflict a bit here and there. I do understand vapor pressure, warm side is where the vapor pressure is, a bit about dew point relative to the temperature of sheathing surfaces, etc, I'm getting fairly good with all that. I suppose maybe at this point, I'll probably just end up picking something and hoping it works. I will likely be doing something very similar to what Mforget describes, a 2x4 stud wall, sheathing the exterior, blowing in cellulose. Those Dow SIS panels are very interesting, I'm wondering if Insul depot has any of those? I'd still be kind of apprehensive to sheath with just those panels still though even though they look good and all. --- well i talked to my rep, they don't have the SIS panels, so that's a no go, looks like osb and something on the outside of that. By the way, for all you SIP guys out there, i got respect and all, but dude, I'm in flint michigan ok, we do stuff cheap here or it doesn't get done, so unless your SIP panels can be gotten for about a $1 or less per square foot, it's just not feasible, and why would I when I could even build something similar for much less, two layers of osb with 4" of iso in the middle or something over a stick frame, now I'm not looking to start a rant about how sips are better, frankly I really don't give much of a hoot because they are way too expensive. Maybe not for someone who can afford to pay more, but not me, I have to be creative like most people do and stretch my dollar for the most bang for the buck possible, with a limited number of bucks to do it with. I think todd and mforget are on the same page with me there.

so anyway, at this point, I'm wondering about the strength of iso, and how it stands up against vapor pressure etc as far as the material itself, not using any facing. Essentially what I'm most concerned with, is if I didn't use purlins or something like that, would it be strong enough to walk on without damaging it while laying it out, possibly in two layers, and while we tape and seal it all up, and the same idea putting siding over it, etc. and is xps that much stronger?
aeridyneUser is Offline
New Member
New Member
Send Private Message
Posts:60

--
08 Sep 2009 01:34 PM
and apparently the sandwiching idea is not a bad one;

http://www.greenbuilding.com/green-building-practices-and-technologies/case-study-net-zero-energy-home-boulder-colorado
JereUser is Offline
New Member
New Member
Send Private Message
Posts:57

--
24 Oct 2009 09:23 PM
Aeridyne,

I am interested in the DOW SIS panels (in place of 1/2" osb) too for my next house. If I use the SIS panels, I'm debating if I want to go with 2x4 or 2x6 walls with closed cell spray foam.

Also looking into staggering the 2x4 studs using 2x6 top and bottom plates OR a double 2x4 exterior wall. With the double 2x4 exterior wall, HVAC ducts can be ran in the double wall (inside one) to the 2nd floor in the case where you have an open floor plan and not too many interior walls. Both of these methods greatly reduces/eliminates the thermal bridging through the studs... plus with the use of SIS panels on the outside, this would provide even more of a thermal break and insulate the outside of the bond and window/door headers.

I owner built the house that I am in now about 6-7 years ago. I'm in Ray Twp., Mi. which is about 45-60 minutes from Flint. The company that I used was Pierson Gibbs Homes www.p-ghomes.com in Richmond.
jonrUser is Offline
Advanced Member
Advanced Member
Send Private Message
Posts:545

--
25 Oct 2009 09:11 AM
I was recently looking at a stick built house that I understood to have walls of:

drywall
vapor barrier
cellulose
1" spray foam
OSB
rigid foam
siding

It was an experienced/quality builder but no idea how well it is working.  I understand that the OSB is optional, except at the corners (to prevent racking).
You are not authorized to post a reply.

Active Forums 4.1
Membership Membership: Latest New User Latest: NewtonDistributing New Today New Today: 4 New Yesterday New Yesterday: 18 User Count Overall: 17307
People Online People Online: Visitors Visitors: 546 Members Members: 65 Total Total: 611

GreenBuildingTalk

Welcome to GreenBuildingTalk, the largest, most active forum on green building. While you can browse the site as a guest, you need to register in order to post.

Register Member Login Forum Home

Search Directory

Professionals Products

Get Free Quotes

Tell us about your building project and get free quotes from green building professionals. It's fast & easy! Click here to get your free quote.

Site Sponsors

For Advertising Info:
Call 866-316-5300 or 312-223-1600

Professionals Serving Your Area:

Copyright 2010 by BuildCentral, Inc.   Terms Of Use  Privacy Statement  Free Quotes  Professional Directory  Advertising Programs