I haven't looked too closely at it or done the math on what it would take, but I've often thought that a reasonable stack with a turbine vent on the top hooked up to the exhaust port of an HRV's heat exchanger might get the air exchanges you need in a coastal wind zone.

This approach has worked as an effective enhancement for slab-depressurization (radon control) systems, which are a lot higher head than any mere ventilation system. Typical turbines for 4-6" stacks pull on the order of 100-150cfm in 5mph type winds.
At the very least it lowers the impedance of the HRV exhaust, lowering the load on the motor. It may make balancing the HRV pressure a bit tricky (or impossible) though.
It'll put the house under significant negative pressure in a high wind, so it's best if any combustion appliances are direct-vent/sealed combustion to fully avoid backdrafting conditions.