Dana - thank you for the thorough response. Your answer gave me a few more questions though...
1 -
It's important to use an air-tight underlayment between the EPS and the t & g roof deck for overall performance reasons
- Would a sheet of Tyvek house wrap do? What type of product do you recommend? Also, isn't the EPS an air barrier? I as going to seal all the edges and corners with great stuff or something similar.
2 -
A better solution for zone 5 is to install a smart vapor retarder (Certainteed MemBrain or Intello Plus) between the interior gypsum and the cellulose, and design in a "rainscreen" gap between the exterior sheathing and the siding
I was planning on an exterior rain screen, but are you saying I wont need an interior vapor barrier at all? And rather just a retarder?