Hi,everyone. I'm working on a sips project, floor panels are designed as the below table,I've never done this before,so what do you think? is the floor panel designed ok? please let me know your answer, appreciate !
Floor Panel (4Ft*12Ft)
OSB Thickness(inch) EPS Core Thickness(inch) Panel Thickness(inch) Double SPF Spline Deflection(inch) Span(Ft) Load(PSF) 0.4685 9.252 10.2 2in*10in*12Ft L/240 12 62.8
|
|
|
|
|
|
|
Greg Freyermuth
 Basic Member
 Posts:131
 |
| 03 Mar 2010 10:44 PM |
|
Whomever you are buying your SIPs from should have this table to help you decide on the layout. They should have tested the panels and should be able to tell you whether the Load is too much. The span is not the problem, the weight is. Typically a floor is L/360 and a roof is likely to be no stiffer than L/240. Hope this helps. |
|
| Greg Freyermuth<br>915-256-7563<br>[email protected]<br> www.energreensips.com |
|
|
cmkavala
 Veteran Member
 Posts:4327

 |
| 04 Mar 2010 06:47 AM |
|
Ivan;
a double 2 x 10 spline is the same as 2 x 10 joists @ 24" oc, at a 12 ft. span would also provide the same support, unless you just need the extra insulation, I don't see the point of the SIP floor |
|
| Chris Kavala<br>[email protected]<br>1-877-321-SIPS<br /> |
|
|
IvanDrew
 New Member
 Posts:12
 |
| 05 Mar 2010 10:28 PM |
|
Greg,thank you for your tips,although i still got a little confused, I've found a load table and sent to your e-mail, would you please check your email and let me know "is it what you're talking about? |
|
|
|
|
IvanDrew
 New Member
 Posts:12
 |
| 05 Mar 2010 10:37 PM |
|
Chris, what do you mean by "i dont see the point of the SIP floor panel"? are you trying to tell me the floor panel i've shown you is not safe or something else? i've sent you an email,please chek it. |
|
|
|
|
SimonD
 Basic Member
 Posts:113

 |
| 07 Mar 2010 12:55 AM |
|
If your application is an 'ordinary' residential one then your design is ok. Typical residential floor loads per square foot are 40lbs live + 10lbs dead(floor framing) + 5lbs dead(wall framing) for a total of 55lbs. If you are going to use tile as a floor finish, the deflection should be L/360 or it will crack, but if your SIP can support 62.8lbs at L/240 then you are probably ok for tile if you add underlayment. However, if your application is commerical you may be very under designed. |
|
| Building Designer<br>PANELfusion, LLC, Tampa, FL<br>simon@panelfusion(dot com)<br>"Metal SIP Advocate" |
|
|
Greg Freyermuth
 Basic Member
 Posts:131
 |
| 07 Mar 2010 02:09 PM |
|
Simon is right and what I meant by typical floors need to be stiffer. We use a lot of tile in the Southwest and the grout is the problem. You proivde a floor with less than a L/360 and you are asking for problems. I will look at the table and get back to you...
|
|
| Greg Freyermuth<br>915-256-7563<br>[email protected]<br> www.energreensips.com |
|
|
IvanDrew
 New Member
 Posts:12
 |
| 07 Mar 2010 07:17 PM |
|
SimonD, this is a residential floor, and i woul like to use tile, about the deflection , i think i will take your advice, finally, thank you so much! |
|
|
|
|
IvanDrew
 New Member
 Posts:12
 |
| 07 Mar 2010 07:27 PM |
|
Greg, i've got your reply, i think i know what to do now, thank you for all the info. you guys are so kind. |
|
|
|
|