Posted By jonr on 05/25/2009 12:16 PM
Using the Geolink software, I don't see much difference in vertical vs horizontal loop lengths. The grout on the vertical has a similar effect as additional tubes or slinkys (contact with more soil). But you could grout a horizontal loop too.
I've seen references to ground water flow being a factor in vertical loops. This would argue that it is best to maximize the amount of vertical loop that is in sand or gravel (ie, 2x200' holes might outperform one 400' hole if you have sand from 100' to 200').
Except for these two issues, I would expect no difference between a 30' horizontal loop and a vertical loop.
If soil and weather were constant and predictable, you might be right, but as they are not, a horizontal loop must be built for extremes that a vertical loop will not be affected by. Soil issues close to the surface may not affect vertical wells, so our horizontals may run as much as 600' longer than verts, I don't think you can credit the grout with 3 times the soil contact (remember there are 2 pipes per bore). -18* in MI causes long operating cycles that affect both types of system, but it also affects shallow ground temps with little impact on verticals I don't think you'd find grouting would get it done on a short horizontal.
The difference between paper engineering and contracting is provision for the uncommon. Most formulae don't include that.
I say this because you seem to be trying to "nut-shell" ground loops which can be done to some degree, but you have to remember all of the components of the equation. Loop designers will often have a X'/ton rule that they use. This results in oversized loops in many situations, but why throw away 50' of pipe/ton if you have a 600' roll and only 550' is indicated?
Good Luck,
J