You guys are AWESOME it is nice to get good information from people that can say something other than "it has to be your flow". thank you!!
So I got out the soldering iron and soldered the jumper back together and verified it with the ohm meter.
System still locks out with the run cycle in the picture below. (with only one pump at ~4psi drop = ~14-15 gpm). The cutout happens at the point that is being measured, so the temp readings accross the board are at that point in time. ALSO the fantastic hot air that it is producing is actually from the 10kw backup strip NOT the unit itself.
I will have the service guy perform the suggested checks and definitely feel confident enough to stand my ground with the tech to see to it that this thing starts acting appropriately
Bad Geo Unit.. No cookie for you!!
Anyhow thank you again for the fantastic support. I'll update the results of the tech visit when he makes it out here.
I wish I had had my system monitor installed when the system was working so I could just reference back to then and know how it used to function.