Hi Dteltech,
It sounds like you'll find this paper interesting if you've not seen it:
[b]con76: A Four-Year Site Measurement of Heat Flow in Slab-on-Ground Floors with Wet
Soils[/b] H.A. Trethowen and A.E. Delsante
http://www.branz.co.nz/cms_show_download.php?id=78Notice the time scale!
I also love this subject, and agree with you entirely. It seems to me that very few people (here in NZ at least) even consider their site conditions.
Have you checked the deep soil temperature for your area? I understand it varies from place to place, and obviously has quite a large effect on heat loss through the slab.
"At soil depths greater than 30 feet below the surface, the soil
temperature is relatively constant, and corresponds roughly to the
water temperature measured in groundwater wells 30 to 50 feet deep.
This is referred to as the “mean earth temperature.” Figure 2 shows the
mean earth temperature contours across the United States. In Virginia,
the mean earth temperature ranges from 52ºF in the northern Shenandoah
Valley and Winchester area to 62ºF in coastal Tidewater."
Earth Temperature and Site Geology
http://www.geo4va.vt.edu/A1/A1.htm#A1Sec2
ARCHIVED Deep Soil Temperatures at select NDAWN stations
http://www.ndsu.edu/ndsu/ndsco/soil/index.html
Steve
PS I hope you are going to publish your results. I'd love to compare them with my modelling. It's the only way to know if the 'theory' is right.