First Floor Insulation Requirement
Last Post 04 Jan 2009 05:49 PM by Brock. 5 Replies.
Printer Friendly
Sort:
PrevPrev NextNext
You are not authorized to post a reply.
Author Messages
BruceUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:142

--
03 Dec 2008 10:00 AM

I'm wondering what is the recommended insulation amount in the first floor of a house in central Indiana when using radiant tubing? Assume that it has  full basement built with R22 ICF walls and 2" of EPS insulation under the basement slab.  The basement will be heated.  Builders don't use any insulation when using forced air heat.    Does that change if the heating method is radiant?

Thanks,
Bruce

Dana1User is Offline
Senior Member
Senior Member
Send Private Message
Posts:6991

--
04 Dec 2008 09:18 AM
Unless you put some insulation between the radiation that responds to the first floor and the basement space, every time the first floor zone is on it'll be heating the basement. In most installations MORE heat would end up in the basement due to the insulating effects of finish flooring, carpets, furniture, etc.

In a fully conditioned basement a radiant-barrier ~1" below the floor and R11-R13 batting should suffice. (NRT.Rob will probably recommend more. :-) ) R-19 batts/no-radiant barrier would perform similarly. R10 of iso board or XPS would be fine too. But it DOES need something or the basement will likely become essentially an uncontrolled somewhat overheated zone.

BTW: Builders SHOULD use insulation on the forced hot air ducts, even within conditioned space, at least on the outbound side. R6 is a mandatory minimum in some locations. But they should also seal all the joints with mastic and pressure test 'em for leakage too, but only in CA is it mandated by law.
njwoodsUser is Offline
New Member
New Member
Send Private Message
Posts:1

--
30 Dec 2008 02:48 PM
hello all,
Well, very informative as usual. I did not remember to check the State to state regulations yet.

Thanks for the reminder that they can be different building codes and regs in each place you wish to build or renovate.

I hope to have a home with radiant floor heating soon.  It has been a very cold winter for much of North America and it would sure feel good.


When you need answers and need them fast.....flooring and carpet
BrockUser is Offline
Advanced Member
Advanced Member
Send Private Message
Posts:599
Avatar

--
30 Dec 2008 03:34 PM
We also have un-insulated radiant tubing under the main floor with the unfinished basement below it, but used as a guest bedroom / kids playroom with a family room / kids playroom. I haven’t been heating the cement floor, but since the radiant from the floor above is not insulated it is warmer down there. A question I have is if we insulate under the tubing will more heat actually go up? Or does it really just limit the heating of the space below (because we want it to do that). I do understand the control side of this, if we did heat the basement floor warm as well I am sure it would get warmer down there than the main floor.
Green Bay, WI. - 4 ton horizontal goethermal, 16k gallon indoor pool, 3kw solar PV setup, 2 ton air to air HP, 3400 sq ft
dmaceldUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:1465
Avatar

--
01 Jan 2009 10:01 PM
Posted By Brock on 12/30/2008 3:34 PM
A question I have is if we insulate under the tubing will more heat actually go up? Or does it really just limit the heating of the space below (because we want it to do that).

Yes and no. The amount of heat that moves from one region (the hot water tube) to another region (the room above or below) depends on the temperature differential and thermal resistance in the path. If you add insulation under the tube and keep the tube temperature the same as it is now, less heat will move into the space below and the same amount will move into the space above. What you will find is you input less heat into the water at the heat source thus cutting down the total heat load. If you continue to inject the same amount of heat into the water as you do now, the insulation below the tube will cause the tube temp to go up. That will drive more heat into the space above. Your control system regulates the temperature of the water in the tube, right? Does this help?
Even a retired engineer can build a house successfully w/ GBT help!
BrockUser is Offline
Advanced Member
Advanced Member
Send Private Message
Posts:599
Avatar

--
04 Jan 2009 05:49 PM
I am circulating the water from the pool through the tubes, it is at 89F so that stays the same no matter how much I am pulling out. I do notice if I run the pump in low speed the water leaving the tubes will be 85F with the pump in high speed the water leaving will be closer to 87F. So I am guessing in my case I would just get a higher return temp on the tubes if I insulated under them and a cooler basement. I do plan to insulate it before the ceiling goes in.
Green Bay, WI. - 4 ton horizontal goethermal, 16k gallon indoor pool, 3kw solar PV setup, 2 ton air to air HP, 3400 sq ft