what do I use for Back up in case of power failer for El boiler infloor radiant
Last Post 04 Jan 2009 10:06 AM by BillN. 1 Replies.
Printer Friendly
Sort:
PrevPrev NextNext
You are not authorized to post a reply.
Author Messages
StephanieUser is Offline
New Member
New Member
Send Private Message
Posts:1

--
03 Jan 2009 09:21 PM

We live in Canada....cold winters. I have a bungalow on a 4ft slab...approx 2600sq ft living space inc the garage. It is a hydra electric boiler for our infloor heating....only source of heat. House was just built a year ago. If the power was to go out like several years ago for 4 days what should we have as a backup......would it only be generator......I need it to run 20 kw if Im not mistaken. Any information would be appreciated.

BillNUser is Offline
New Member
New Member
Send Private Message
Posts:53

--
04 Jan 2009 10:06 AM
You probably don't need 20 kw as a backup. I am sure that 5 to 10 kw will keep the house from freezing. You just have to figure out how to limit the boiler for asking for more than you have to give.