Posted By kicker_92 on 04/13/2009 3:47 PM
Posted By NRT.Rob on 04/13/2009 2:56 PM
I would not use a water heater for that load. I would use a mod/con boiler. with your degree day count it's getting more marginal, but you're still probably talking about 150+ therms/year difference.
I should have also included, our gas costs are $1.031/therm ($9.772/GJ), and electrical is $0.0615/KWh.
What about something like the Takagi T-K3? I could go to a pair of those for the radiant and DHW.
One feature that has me hesistant to go with a boiler is that we are doing a heated shower surround on a seperate zone (so actually a 4 zone system). This will short cycle a flash heater with such a small flow and heating demand.
Posted By NRT.Rob on 04/13/2009 2:56 PM
I would not zone by pump. I would run the whole system on one pump
So would you setup a manifold with zone valves instead? I'm open to either system, and since it's not much flow a single pump works too. I'd been thinking a set of four Taco 007's for the current layout. Maybee using variable speed pump for the whole system instead?
Posted By NRT.Rob on 04/13/2009 2:56 PM
And I would redesign the house for more wintertime passive solar gain...
Unfortuantly with this lot it's not an option. We may include soem skylights, but thats about it for south facing glass.
Posted By NRT.Rob on 04/13/2009 2:56 PM
All this assumes "best value" and not "I like the tech" is the goal.
I do like the tech, but this is a house for my wife and I to live in for the next 50-60 years
, so reliability is much more important. Hence the appeal of a standard off the shelf hot water tank.
Thanks for your input!
Why a PAIR of TK3s? A single, with the zone control & heat exchanger loop set up for DHW priority should handle a load like this just fine. Unless you're a hot-water hawg, a smaller (more appropriately sized) mod con + an indirect would probably come in at comparable money (or lower) than TWO TK3s.
If for the DHW end you go with a "reverse-indirect" (eg. TurboMax, Everhot EA series, ErgoMax) set up as a buffer for the heating system you can't possibly short-cycle the burner, whether a boiler or a Takagi, or whether for micro-zones or DHW draws. Hand washing draws- anything under 2 gallons/draw @2gpm on a TK3 are typically under 50% efficiency- half the heat is lost up the flue during flue purges, and at low-flow low-fire it's at it's lowest combustion efficiency durign the draw. (This is the very definition of "short cycle"!) But maintaing a buffer tank or indirect you'll hit 82-85%, minus a very small standby loss (as compared to a standard tank HW heater.) Maintaining an indirect at 130-140F+ for DHW with a mod-con cuts into condensing efficiecy limiting it to about 87-88%, but reduces cycling losses- the actual difference may/may-not be negligble. But it'll INCREASE the efficiency of a tankless by minimizing the short cycles, and boosting the burn rate into a higher combustion efficeincy zone. If you go with a mod-con you may prefer a different topology to max out on space-heating efficiency by being able to run at lower than DHW temps much of the season, but with a tankless, a buffer-centric zone with no short-cycling on DHW draws will be more efficient, and puts less wear & tear on the tankless.
A single ECM pump + zone valves will likely end up using about as much electricity as 1-2 Taco-07s.
An indirect tank will outlive any standard gas-fired tank by a factor of at least two.
If you go with an indirect fired tank NOT set up with priority controls, it'll probably still do fine at the space heating loads you're talking. But if you can set up the main shower drain with a drainwater heat recovery heat exchanger that pre-heats the cold feed to both the indirect and the shower (or the whole house), it's like adding 25-30KBTU to the burner while taking a shower (but not for tub-fills, since you need simultaneous water & drains flows to get the heat exchange.) GFX/PowerPipe/Retherm are the easiest to find in the US. Bigger is better (both length and diameter) for improving the performance, but even a 36" x 4=incher is usually good for ~50% heat recovery at shower flow rates. They're extremely low maintenance, and use no fuel- if you have at least 36" of vertical drain downstream of the shower to tap into, it's a no-brainer, if you're looking at the long-term view, or even the short term view, if it means you can now go with a 60KBTU/h boiler instead of a 100KBTU/h boiler.
Should you decide to go with the TK3 instead of a boiler you need to be aware than it's combustion efficiency at lowest fire (11KBTU) it likely to be well below it's mid-modulation efficiency. I don't KNOW that it's a problem with the TK3, but I have 2nd hand reports that running another tankless at under ~20kbtu/h for long periods in conjunction with an air handler coil (140F out, ~115F return) resulted in rapidly destructive condensation on the copper heat exchanger. (The TK3 is also a copper HX.) Setting it up for either higher minimum fire or return temps of 125F+ would probably keep both the efficiency higher and the self-destruction risk lower. (I'm still looking into this. Woulda thunk that something designed to handle 40F water in from the street with 110F output could manage just fine forever with 115F return water.) Tankless HW heaters in mid-modulation typically run ~83-85% combustion efficiencies (with jacket losses, more like 82%), but at high-fire run a bit higher. I'm not sure how low the TK3 gets at its lowest fire, but at some point the fire is slow low that there's insufficient turbulence on the heat exchanger for good heat exchange and the stack temp goes up. It wouldn't surprise me that a 200k burner like the TK3 is only getting ~75% efficienecy at 20KBTU/h in (10% of full-on), and sub-70% at the 11K. (Just a WAG- don't have 3rd pardy data, haven't tested it myself, but it's not much different than any other copper water-tube boiler.))
A boiler with a stainless heat exchanger will probably last longer (at 3-5x the cost of a tankless), but they all have maintenance issues- not nearly as "set & forget" as higher temp heating systems and sub-83% combustion efficiency boilers. A ~50KBTU 80-82%AFUE cast-iron beast could run DHW-temp central reverse-indirect/buffer system too, as long as you plumbed it with enough boiler-bypass to keep the return water to the boiler above 130F to protect IT from destructive condensation. And with drainwater heat recovery it's likely that 50-60K would be all you ever need. (Was your heat load calculated, or measured? Manual-J etc have built- in margin- your actual heat load could be as much as 25% lower, in which case even an 80% AFUE 60K boiler would be oversized.) Odds are good that if you set up the nominal output of the TK3 to ~30-35K and run it with a buffer it'll beat the cast-iron beast with some margin. The cycle losses of the lower-mass burner are lower, as are the jacket & flue standby losses, and since it'll be modulating somewhat the burn times/duty cycle are longer- long enough to make a total as-operated efficiency difference.
The system currently being installed in my house (as yet untested & tweaked- no actual performance data to report):
*~30KBTU design day heat load
*5 zones of staple up- (I need 130-140F water much of the season) w/ single ECM pump + zone valves
*ErgoMax indirect-DHW/buffer (central buffer to system, no priority controls)
*Takagi KD20 as heat source, running circulating boiler water, not potable water (and if it craps out in 3 years I'll just
find something better- it was cheap :-) Most in the field have lasted
longer- don't know it's actual expected lifespan in heating apps, or in
this system topology.)
*4"x 48" PowerPipe drainwater heat recovery (cheaper than marital
counseling, should I happen to be the first one to shower on a -7F winter
morning. :-) )
I'm sure by March I'll know a lot more about how well this
actually works, eh? ;-) I intend to measure it's combustion efficiency at a couple of burner output points to avoid falling off the low-fire efficiency cliff without going to a ridiculously low duty cycle. (I may wing it and measure just flue-gas temps rather than a full-on gas component analysis, since that's easier to do and will likely be "good enough" for my purposes.)