We have not made the decision if we're going with radiant heat for the whole house or not. We plan for it in the basement, but we're looking into it for the main floor.

One question that I have is, if we do go with whole house radiant, what would my options be for A/C? And we're building as tight as we can, so I think some sort of ventilation system (ERV/HRV?) is a given. I live near Ames, IA.

Any ideas?
Dana1User is Offline
Senior Member
Senior Member
Send Private Message
Posts:6991

--
27 Oct 2009 09:57 AM
If it's well insulated & tight, with good shading on your south facing windows in summer, your primary AC load will be humidity:

http://www.climate-zone.com/climate/united-states/iowa/des-moines/

The average relative humidity in June/July/August is 68/70/72%, when the average temps are 72/77/74F for the correspondingly. Well insulated & with minimized solar gain the average temp of the house will be only a few degrees F above those averages just coasting- you won't have much sensible load at all. But to stay healthy & comfortable you'll need to keep the indoor humidity under 60%, and with cooking, showering, sweating & breathing it'll be well over the outdoor RH, even with an HRV. Outdoor air will not be sufficiently cool or dry to get by with night-time ventilation strategies in your case. If it's an open floor plan or you can keep all of the interior doors open you may be able to get away with a single small window air conditioner or a basement dehumidifier. Otherwise a whole house dehumidification/cooling coil in the HRV ducting as a whole house dehumidifier will get you there.

In my less-tight less-well insulated house in a slightly cooler but somewhat more humid climate I use a portable 500 Watt dehumidifier in the basement that controls the humidity for the whole house fairly well most of the summer. We have central AC (about 6x oversized for the load), that we run fewer than 10 hours/year, but we can as-easily keep the place comfortable with a half-ton window air conditioner in an upstairs room to handle the sensible load. When I'm done insulating the roof we probably won't even need that, but the dehumidifier will still have a significant July/August duty cycle- yours will too.
Boontucky-girlUser is Offline
Basic Member
Basic Member
Send Private Message
Posts:250

--
28 Oct 2009 10:49 AM
Thanks for the reply Dana1.

What would be considered good shading on the south facing windows? We have 2 ft overhangs all around our house (except gables), and our south windows face SE and SW. On the SE ones we have four 50 ft tall oak trees about 50 ft away from the house, that do give quite a bit of shading, but I can't remember what % of the day the shade actually falls on the house.

This past summer, our eaves were open since we don't have most of the soffit and no ceiling installed, and in the basement (ICF) those few days we had that were really humid and hot it was nice and "cool" down there. It was the upstairs (2x6, no insulation) that felt stuffy, but not really hot. So what you said really makes sense.

So depending on the cooling loads, if our sensible load is small, we might be able to get away without an A/C unit and just have an HRV and something to deal with the humidity. Or do I still need to have some sort of A/C unit in the setup?

About the HRV, how do you decide if it is an HRV or ERV what we need to look into?

So we might be lucky enough that we wouldn't really need AC, and we should focus on ventilation and dehumidifying the house? That would be sweet.
sgo70User is Offline
Basic Member
Basic Member
Send Private Message
Posts:125

--
28 Oct 2009 09:47 PM

 I had the same question along with some others but I don't want to take over yours Boontucky. Dana, do you have any more links or info on this:

"whole house dehumidification/cooling coil in the HRV ducting"
 
I'd like to find out more and see if that would work in my case.

Thanks,
Sean

Dana1User is Offline
Senior Member
Senior Member
Send Private Message
Posts:6991

--
29 Oct 2009 10:44 AM
Posted By Boontucky-girl on 10/28/2009 10:49 AM
Thanks for the reply Dana1.

What would be considered good shading on the south facing windows? We have 2 ft overhangs all around our house (except gables), and our south windows face SE and SW. On the SE ones we have four 50 ft tall oak trees about 50 ft away from the house, that do give quite a bit of shading, but I can't remember what % of the day the shade actually falls on the house.

This past summer, our eaves were open since we don't have most of the soffit and no ceiling installed, and in the basement (ICF) those few days we had that were really humid and hot it was nice and "cool" down there. It was the upstairs (2x6, no insulation) that felt stuffy, but not really hot. So what you said really makes sense.

So depending on the cooling loads, if our sensible load is small, we might be able to get away without an A/C unit and just have an HRV and something to deal with the humidity. Or do I still need to have some sort of A/C unit in the setup?

About the HRV, how do you decide if it is an HRV or ERV what we need to look into?

So we might be lucky enough that we wouldn't really need AC, and we should focus on ventilation and dehumidifying the house? That would be sweet.

Seasonal exterior shades are best (got any large deciduous trees to plant? :-) )  The 2' over hangs are good, but if they don't shade all of the S-facing glazing for most of the middle of the day in July you'll still be getting significant solar gain when you want it the least.  (I have 2' overhangs, and they shade my kitchen windows optimally, but living room, not so much.) Getting it to fully shade the very bottom of the windows usually requires a bit more.

Some people build vine trellises, grape arbors, etc for semi-automatic seasonal shading, others use exterior roll down shades:

http://www.builditsolar.com/Projects/Cooling/Rollup4.jpg


http://www.builditsolar.com/Projects/Cooling/Rollup3.jpg

ERVs have slowly rotating dessicant wheels to exchange humidity between the incoming & outgoing flows.  HRVs have heat-exchangers only.  ERV will lower the load on your dehumidifier in summer, but will make it more humid in winter.  In very tight houses in IA it's rare that you'd ever drop below 30% RH in winter anyway, so HRV may be a better choice- depends on just how tight the house REALLY is.  (Using humidity sensing control you can have it automatically slow the ventilation rate if the humidity drops too much in winter. Or you can adjust duty-cycles as-needed.)  At only ~1000 annual cooling degree-days in a moderately humid environment you're somewhat on the edge of ERV vs. HRV- there's no clearly "right" answer.  But either way, get the smallest one that meets the ventilation requirements, and one with high efficiency motors.  ERV/HRVs are a constant background load to the power grid, and they're not all created equal.

A small window AC unit may be a good fallback position.   If solar gains are well controlled and it's a well insulated tight place, your average temps are not super hot in any given month, but they can soar for any given week in the summer.  If you do go central AC, undersizing it and running it with both temperature & dehumidistat control will optimize efficiency & comfort.  (I suspect a 2 ton unit would be overkill here, 1-ton is about as low as central AC goes, and even that might be too big.)  It's fine if it doesn't keep up with the sensible load, since it probably won't break 85F on the worst day, and with a 100% duty cycle the RH will be well under 40% when it does. 

Whether whole-house dehumidifer or central AC, if you have dust-mite allergies setting the dehumidistat to 50%RH is good, otherwise 60% is comfortable enough up to ~78-80F, and sufficient to mitigate mold hazard.