TechGromitUser is Offline
Registered Users

Posts:221





02/18/2008 3:56 PM  
I've been told that insulating my basement would save between 20k to 27k BTU of heat loss. My initial response was doubtful, since the basement isn't heated anyway. When I thought about it, since the basement is cooler than the 1st floor above it, it would tend to cool off the first floor faster then it should. I know that 20k BTU is just a rough estimate, but is there a formula I could apply to figure out what my actual BTU heat loss currently is. I would think that a 10 x 20 foot uninsulated basement would have the same heat loss per sq foot as a 20 x 50 uninsulated basement. And number two, how much can I expect to save per 1k BTU heat loss if I insulated the basement. This would give me a cost / benifit ratio I can use to justify the expense of insulating.

geodeanUser is Offline
Registered Users

Posts:583





02/18/2008 4:35 PM  
Attached are two heat loss calculations from a house.  The first has no insulation in the floor.  The second has R 30 in the floor.

As you can see the difference is about  20k BTUh.

This is for total floor footage of 2700sqft.

1 kw is about 3400 BTU.  If your heat pump has a COP of 3 then you get about 10k BTUh for each kw you buy.  So based on your kw rate,  you can figure your savings.

Hope this helps.

Attachment: no floor insulation.pdf
Attachment: with floor insulation.pdf


Dewayne Dean
PalaceGeothermal.com
Why settle for 90% when you can have 400%
We heat and cool with dirt!
visit- http://welserver.com/WEL0114/- to see my system
TechGromitUser is Offline
Registered Users

Posts:221





02/18/2008 7:23 PM  

Thanks for the PDF files! Over what period of time are these figures for? Daily Averages?

Thanks!

 

geodeanUser is Offline
Registered Users

Posts:583





02/18/2008 7:26 PM  
These are BTU's per hour at the design conditions listed at the top of each report.

This particluar house was designed for an outside temp of -10° F.   So when it is -10  the heat loss will be what is listed on the report.

Dewayne Dean
PalaceGeothermal.com
Why settle for 90% when you can have 400%
We heat and cool with dirt!
visit- http://welserver.com/WEL0114/- to see my system
You are not authorized to post a reply.



ActiveForums 3.6

Professionals Serving
Your Location:

Creative Panels (Kingsburg, CA)
Amvic-Pacific (Nevada City, CA)
Sierra SIPs (San Andreas, CA)
Blue Lupin Developments (Incline Village, NV)
Greenblock Worldwide Corp (Cave Creek, AZ)
View More

GBT Project Albums:

efficiency (Old Town, ME)
Off-the-grid home (E of Eganville, ON)
Jay's House (Burlington, VT)
MN Geothermal Retrofit (Twin Cities, MN)
Kitchen/gathering room (Manchester, MI)
More Info |  Search
Copyright 2008 by BuildCentral, Inc.   Terms Of Use  Privacy Statement