anyone here familiar with the Earthlinked system? I have a few questions as to the manifold where the ground loops tie in. Does it have to sit up upright in the ditch??


                                                                        Thanks, Brian
joe.amiUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:4377
Avatar

--
19 Nov 2008 10:18 PM
I'm not sure I understand the question, Brian, but while refrigeration piping has some limits, it is relatively indifferent to direction. Direction and length can pair for oil recovery issues if installation instructions are not followed.
Tell me what you mean by "upright".
Joe
Joe Hardin
www.amicontracting.com
We Dig Comfort!
www.doityourselfgeothermal.com
Dig Your Own Comfort!
tuffluckdrillerUser is Offline
Advanced Member
Advanced Member
Send Private Message
Posts:630
Avatar

--
20 Nov 2008 12:25 AM
I replied last night, but nothing posted....

The manifolds need to be level, if it's the EarthLinked product. This means that the main lines coming to the manifold will connect to the top or bottom of the manifold, depending on which way you orient it. The important thing is that the brass piece of the manifold is as close to level as you can get.
Clark Timothy ([email protected])<br>Geothermal Heat Pumps: Heating and Cooling that's Dirt Cheap!<br>www.pinksgeothermal.com