Duct size effect on geothermal sizing
Last Post 16 Apr 2009 12:37 AM by joe.ami. 4 Replies.
Printer Friendly
Sort:
PrevPrev NextNext
You are not authorized to post a reply.
Author Messages
mjablonsUser is Offline
New Member
New Member
Send Private Message
Posts:6

--
15 Apr 2009 09:54 AM

This site has been a great reference as I've been investigating replacing my 20 year old gas furnace and a/c.  I've gotten a couple quotes with widely differing sizing.

I currently have a 2.5 ton electric AC.  I've had one contractor say the maximum size geothermal system my ducts can handle is 2.5 tons and that I would need to rely significantly on supplemental heat.  Another one though three tons would be fine, while a third thought four or five tons could work just fine through my ducts.  Obviously- I have major issue in the variety of load calculations (or lack of calculations with guessing).  I recall a thread mentioning sites where you could do your own manual j and a few offers that experienced folks might be wililng to calculate a manual j for ~$50.  If I didn't have a split level house, I'd do the calculation myself, but I've heard that the split levels have to be tweaked in the tools more than a standard house and I want to make sure I get this right.  Would anyone be interested in doing a remote (or local) manual J?  I can provide a floor plan, measurements, and some insulation level details along with 3 years of utility analysis.

But, ignoring my actual heat load needs for the moment, this brings up an interesting question that I haven't seen much about on the forms:
How does a home's existing duct work affects the maximum possible system sizing.  Is it the number of registers and returns?  The volume of the outgoing and return ducts at the furnace?  I know that compared to a gas furnace, geothermal blows lower temperature air at higher speeds.  I'm not sure how the temperature or speed would compare to an electric a/c unit.  Are there measurements I can take that would facilitate the discussion? 

- Marty

tuffluckdrillerUser is Offline
Advanced Member
Advanced Member
Send Private Message
Posts:630
Avatar

--
15 Apr 2009 11:21 AM
Marty,

Duct size is not the only issue. The fittings and equivalent length of the installed duct has a lot to do with it, too. The duct sizing could be just fine and have bad fittings. Example would be an elbow in the main duct without turning vanes. Or worse yet, tapping the supply plenum from the blower right into the bottom of the supply trunk duct.

I've seen duct installations that make me cringe when it comes to equivalent length (on houses we were installing vacuum systems in, not the duct). One had a 5 ton A/C unit (oversized anyway) that had 24" x 12" duct, both ways from the furnace. This duct size should be adequate for 5 tons. However, because of the fittings they used and their equivalent length (EL), the furthest 3 registers came up to 650' EL, 665' EL, and 685' EL. I haven't been back to talk to the home owners, but I'm guessing they don't get much air to those rooms.

The contractor that did this continues to do it. If he'd just not tap into the bottom of the supply duct with his plenum (not recommended in any application), use turning vanes, and use top takeoffs instead of just using elbows, his systems would be much better. Unfortunately, he just continues, assuming that because it supposedly worked last time, it must work this time, etc....

Anyway, as far as existing duct capabilities, the most accurate ways to measure the duct capability are:

- measure each register's cfm and add them up.
- using the electric furnace (I'm assuming that's what you mean when you say electric A/C), find out the following and plug it in to the equation:
- temperature difference between the supply air and the return air
- kW size of the strip heat
with this info, BTU output = (kW size) X (3413)
Then, CFM = (BTU) / (1.08 X Temp. Difference)

With the CFM, one should be able to look up/find the blower data for the blower you have (brand of furnace) and see what static the duct/blower is performing at. Should be able to then apply a bigger blower and see what that does to static, etc... You'd need someone knowledgeable at this point to weigh higher statics vs. blower power performance, etc.

Hope this isn't too vague...

Clark Timothy ([email protected])<br>Geothermal Heat Pumps: Heating and Cooling that's Dirt Cheap!<br>www.pinksgeothermal.com
tuffluckdrillerUser is Offline
Advanced Member
Advanced Member
Send Private Message
Posts:630
Avatar

--
15 Apr 2009 11:26 AM
There's one more way to get cfm... If you have the blower data for the blower, measure the static pressure difference between supply and return. Look in the blower data charts and see how much cfm is there.
Clark Timothy ([email protected])<br>Geothermal Heat Pumps: Heating and Cooling that's Dirt Cheap!<br>www.pinksgeothermal.com
mjablonsUser is Offline
New Member
New Member
Send Private Message
Posts:6

--
15 Apr 2009 04:13 PM
Sorry for any confusion- I have a natural gas furnace and an electric air conditioner. The furnace is a 110,000 BTU 60% efficiency furnace.

Thanks for the detailed reply. When you say cfm, do you mean cubit feet per minute of air flow? How would you measure this? I don't think I have any data for the blower, but I'll look and see if i can find the model number and look it up online. Supply and return air temperatures will be easy enough. In your equation, is CFM only dependant on the temperatures and the BTU? Or is there a volume flow component as well?

I have two main duct outgoing duct lines (with accompanying returns). The furnace is on my lower level of a split level house. The front half of the house is a single floor above a concrete crawl space. The back half is two levels- half a flight down to the lower level and half a flight up to the upper level. One line goes up from the furnace to the ceiling, and then takes a 90 degree turn through the ceiling to the front half of the house. All of this duct work is in the ceiling of the crawl space below the main level. One main duct runs the length of the first floor with smaller circular ducts running out at 90 degrees to the various registers. No wacky turns or cuts that I can see. The second outgoing duct line goes up to the second floor, but it's in the walls so I can't see how it's run.

Tanks-

Marty
joe.amiUser is Offline
Veteran Member
Veteran Member
Send Private Message
Posts:4377
Avatar

--
16 Apr 2009 12:37 AM
Can do the heat load if you'd like to PM me. Duct capacity depends on lots of things as clark mentioned.
Based on what you told us, I'd guess the 5 ton guy is mistaken.
j
Joe Hardin
www.amicontracting.com
We Dig Comfort!
www.doityourselfgeothermal.com
Dig Your Own Comfort!