Posted By tnlgeo on 07/05/2009 9:51 PM
heat load of 47,300 BTU/hour.
Heat pump is a 4-ton ClimateMaster Tranquility 049 water-to-air, with added 10kW electric coil heater to provide supplemental heat as needed.
Went with a Three zone setup to run the system.
Also added an Aprilaire whole-house humidifier to help with dry winter heating.
If you are not particularly North of Lansing MI, I would say the 4 ton is oversized. What % of the load did your contractor suggest it would handle?
Not a fan of zoning in general, geo in particular and oversized equipment especially (if you are oversized as you appear to be).
I use 3/4" slinkies, and depending on soil, the same number of feet as your loops (though divided into 4 slinkies).
Not a fan of any but steam humidifiers (i.e. Honeywell True Steam or such) if one is required at all. Lower temps of geo make bypass humidifiers less effective. Lower air temps of geo also require less supplemental humidity and in some cases, none.
Now my questions for you....
How many of your installers references did you check?
How long have they been in geo business?
What are their licenses/certifications?
Installing contractors have more to do with customer satisfaction than type of loop field, heat pump, humidifier etc.
Good Luck,