Being familiar with commercial hydronic systems we always design systems with expansion tanks and air separators.
Looking for input on the benefits of a small inline air separator and expansion tank on a residential geothermal system. I figure a small bladder type expansion tank could maintain pressure in the system during seasonal fluctuations/pipe expansion.
engineer
Veteran Member
Posts:2749
11 Sep 2009 09:13 PM
Shouldn't need them. HDPE loop pipe grows and shrinks a bit with temp changes accommodating loop fluid volume changes stemming from temperature changes, and there is no need to separate air if the system was properly purged of air at the get-go.
Curt Kinder <br><br>
The truth is incontrovertible. Malice may attack it, ignorance may deride it, but in the end, there it is - Winston Churchill <br><br><a href="http://www.greenersolutionsair.com">www.greenersolutionsair.com</a>
geotek
Basic Member
Posts:154
13 Sep 2009 06:22 PM
In days gone by expansion tanks were sometimes used, but to keep costs down they are seldom used today in residential. Micro bubbles also form larger bubbles that can be problematic in some loops. It's a cost thing.
craigb93
New Member
Posts:47
15 Sep 2009 09:10 PM
Well, I put both on the ground loop and the load loop(s). In addition there is a high point vent valve on the top of the load supply tank. If you ever have to open the system(s) for a pump change, etc there will be some air to deal with.
Two Exp Tanks and two SpiroVents are about $250 + install. Probably cheaper than a service call to purge in case air is trapped somewhere.
If that's too steep by all means include high point vents. If your layout has the unit in the basement be sure the HP vent is piped to a spot for a bucket if it's inside the house.
Dick
You are not authorized to post a reply.
Green Building Forums
--General Forum - Residential
--General Forum - Commercial
--Green/Energy-Efficient Design and Planning
--Green/Energy-Efficient Building and Construction
Green Building Technologies
--Insulating Concrete Forms (ICFs)
--Structural Insulated Panels (SIPs)
--Radiant Heating
--Geothermal Heat Pumps
--Solar and Wind Power
--Windows/Doors and Interior/Exterior Finish
--Appliances, Lighting and Kitchen/Bath Fixtures
Feedback/Support
--Rules, Instructions and Announcements
--Suggestions/Feedback
--Testing Area
Forums
>
Green Building Technologies
>
Geothermal Heat Pumps
Active Forums 4.1
Membership:
Latest:
croccohvacusa
New Today:
0
New Yesterday:
0
Overall:
35027
People Online:
Visitors:
139
Members:
0
Total:
139