Posted By cleanair08 on 02/03/2008 2:26 PM
Where do you install the pressure sensor? From my understanding the second floor and basement ussually operate at a slight negative pressure and the middle floor (1st floor) is ussually nuetral.
Here's the pertinent section from the installation manual for the PressureGuard option. I found the manual at BlueRidge by Googling UltimateAir PressureGuard manual in case you want to check it for yourself. Considering how well connected a basement and second floor are to the first floor I don't how you'd have them at different pressures without having tight doors and strong fans moving air in or out of the 3 spaces.
Installation
The Pressure Control Option comes with three additional componanents. Two small pressure
taps (static pickup tubes), and the pressure transducer. The pressure transducer must be
mounted in a conditioned space, in the most convenient location for wiring the transducer to
the RecoupAerator, and to connect the transducer to the two pressure taps (see the layout
diagram). It can be screwed to a wall, floor joist, or any other indoor stationary location.
The indoor pressure tap should be mounted to an interior wall, which could be considered the
central most open point in the residence. The outdoor pressure tap should be located on an
exterior wall, which is exposed to the outdoor environment. A garage, crawl space, or attic
space may be a good location for this pressure tap, if either of these spaces are not considered
part of your conditioned envelope and are vented to the outside. Avoid mounting the outdoor
pressure tap in a windy location. You will need to run ¼” tubing (flexible or non-flexible),
from the “hi” port on the transducer, to the indoor pressure tap, and from the “lo” port on the
transducer to the outdoor pressure tap.
Deciding on the Pressure Selection
While wiring to the 3-motor controller at the RecoupAerator, you should now make a
decision about what pressure differential you want the RecoupAerator to control* to. The
main objective (most simply described) is to keep humidity from entering the wall cavities,
which will lead to mold problems. In most installations, you will want to select a ‘balanced’
or zero pressure differential because high humidity levels will oscillate from inside to outside
during the year for a given climate. If your climate has higher outdoor humidity than indoor
humidity all year around, then you should select the 1 or 2.5 Pascal positive pressure
selection. The final position, or the ‘off’, disables the pressure control feature, and allows
the unit to operate as a balanced airflow ventilation system. Make your jumper selection
according to these parameters and the diagram in this manual.
*The ability of the unit to maintain (control) pressure differential is directly dependant on the overall amount of negative/positive pressure
it must overcome.