Posted By zircote on 03/19/2009 5:25 PM
caja715
The amount of solar radiation you can collect each day is going to be very small compared to the amount of heat your house will will need to stay warm.
On clear sunny days you may be able to collect about 50K BTU per day, 2 panel system, your Geo unit is producing 60K BTU per hour.
Tanks are equally useless unless they are the size of large(1 acre) and deep(10-12 feet). There are just not enough BTUs to collect.
Check out the Geo portion of this forum. Also, see
http://forum.geoexchange.org/geothermal-geoexchange-forums/general-discussions/
Your concern should be if your Geo filed entering water temp is getting to low and is causing a lock out.
IIRC, the multiple insulated septic-tank storage used in the Ohio experiments were good for about 10 days worth for a
superinsulated house (this one clearly isn't superinsulated, if it needs a 5 ton compressor on design-day.) They were for a fully solar heated house not a house heated with a 5 ton load heated with an earth-coupled heat pump . I like the idea of a subterranean lake as seasonal solar-storage though. :-)
There are plenty of seasonal BTUs to collect, (the peak 60KBTU/h load should only happen for ~3% of the total hours in the heating season if the contractor did the heat load calc right), it's just hard to store enough for long periods with heating loads that high. To do anything very useful with solar it's more cost-effective to cut the load way back with a high-performance building envelope first, then the required size of the solar technology & storage capacity shrinks to something manageable (as in the Riverdale Net Zero project), and you only need to consider at most a week's worth of storage capacity (with some backup) to smooth it out on the coldest/darkest periods, not a month's worth.
People fall in love with the concept heating their homes with solar from it's low operating costs before doing the math on how much solar capital it takes to actually support the load. For most houses it's hard to make a case for significant-scale solar heating retrofit on a performance basis. If you first get the design-day heat load under 15KBTU/h, (under 10K if you can), it becomes more feasable/affordable.
I like some of the engineering of the Riverdale house, such as the notion of using a small heat pump and a decent sized tank to be able to store heat at room temp (or even well-below room temp), boosting the midwinter performance of the solar collectors in a cold climate by probably 30% or more. This approach was likely cheaper & easier than buying & mounting 30% more collector AREA. (If I ever retrofit my house you can bet I'll be doing the math on that!)