Forums > Green Building Technologies > Solar and Wind Power > Subject: My drainback won't drainback

You are not authorized to post a reply.   
Prev Next
Author Messages
RickardUser is Offline
Registered Users
New Member
New Member
Send a message
Posts:2


11/06/2009 10:55 PM  
I am in the middle of installing a drainback system with evacuated tubes and two pumps. I have a 1/4"+ per foot slope on the panels and much greater slope everywhere else. The system won't consistently drainback fully. There is probably a 1/4 of the water in the system still in the pipes when the pump turns off. I've added a loop from the top of the drainback tank to a couple of feet above the supply side and that helped but it is inconsistent. Would making that loop higher be the answer or a vacuum breaker up high with a air vent on the drainback tank? Any ideas? Thanks in advance. Dean
RickardUser is Offline
Registered Users
New Member
New Member
Send a message
Posts:2


11/17/2009 3:21 AM  
I moved my heat exchanger to the supply side of the tank and that fixed everything. System works great now. Apparently all devices need to be on the supply side of the tank in a drainback system. Dean
You are not authorized to post a reply.
Forums > Green Building Technologies > Solar and Wind Power > My drainback won't drainback