Todd:
It sounds like you are interested in something more accurate than the averaging inherent in ER. Better than the ER is the ERS. I mentioned it in my previous post:
“ There is also yet another variation called ERS or Energy Rating Specific. It uses city specific indoor outdoor temperature differences and orientation specific solar data. This allows orientation by orientation comparisons. “
Before explaining about ERS, I will again remind everyone that:
ER (and ERS) were never meant to predict actual energy use/contribution of a window in your house. Rather like the mileage ratings for cars it’s meant to serve as a comparison between different windows. --- in a heating climate.
If you are interested in predicting energy use, you need a computer simulation tool like; Energy-10, HOT2000 or the like.
However, ERS is still useful. It’s more accurate than ER - because it requires that the 3 co-efficients for sun, temperature and wind be changed for local conditions.
Todd, you’re in Cleveland so I’m going to give you data for Windsor, ON
A) Coefficient for Sun
In the ER equation the average solar gain for a vertical surface is 72.2 W/m^2 (averaged the 211 day or 5064 hr heating season for and average CDN city)
For Windsor the average solar gain by orientation is as follows:
S 121.9
SE/SW 102.2
E/W 67.1
NE/NW 42.0
N 36.6
So Windsor is pretty average, for Canada, when it comes to solar gain
B) Coefficient for Temperature
In the ER equation the average indoor outdoor temperature difference is 21.9 over the 211 day (5064 hour) heating season in degrees Kelvin (Celsius)
For Windsor, ON the average temperature difference is:
19.0
So Windsor is warmer than average CDN city
C) Coefficient for Wind
In the ER equation the Pressure Factor is 0.54
For Windsor, ON the average temperature difference is:
0.344
So Windsor is less windy than average CDN city
(Again, this term has very little meaning for a new window – even with a relatively drafty new window its hard for this term to affect the ER by more than 0.5 W/m^2K)
And that’s probably enough for now
Any questions?
Stephen Thwaites P.Eng. Thermotech Fiberglass Fenestration |