"anything in contact with concrete/masonry needs to be PT or naturally durable wood (redwood) or protected with an impervious moisture barrier"
Sorry Chris, your blanket statement is incorrect, or at a minimum misleading. My comments follow this section from the IRC2003 Commentary used mostly for clarification purposes by Building Officials. (And yes, I am a licensed one).
SECTION R319
PROTECTION AGAINST DECAY
R319.1 Location required. In areas subject to decay damage
as established byTableR301.2(1), the following locationsshall
equire the use of an approved species and grade of lumber,
pressure treated in accordance withAWPAC1,C2,C3,C4,C9,
C15, C18, C22, C23, C24, C28, C31, C33, P1, P2 and P3, or
decay-resistant heartwood of redwood, black locust, or cedars.
1. Wood joists or the bottomof a wood structural floor when
closer than 18 inches m) or wood girders when
closer than 12 inches (305 mm) to the exposed ground in
crawl spaces or unexcavated area located within the pe-
riphery of the building foundation.
2. All wood framing members that rest on concrete or ma-
sonry exterior foundation walls
and are less than 8 inches
(203 mm) from the exposed ground.
3. Sills and sleepers on a
concrete or masonry slab that is in
direct contactwith the ground unless separated from such
slab by an impervious moisture barrier.
4. The ends of wood girders entering exterior masonry or
concrete walls having clearances of less than 0.5 inch
(12.7 mm) on tops, sides and ends.
5. Wood siding, sheathing and wall framing on the exterior
of a building having a clearance of
less than 6 inches (152
mm) from the ground.
6. Wood structural members supporting moisture-perme-
able floors or roofs that are exposed to theweather, such as
concrete or masonry slabs, unless separated from such
floors or roofs by animpervious moisture barrier.
7. Wood furring strips or other wood framing members at-
tached directly to the interior of exteriormasonry walls or
concretewalls belowgrade exceptwhere an approved va-
por retarder is applied between the wall and the furring
strips or framing members.
This section addresses the need for minimum protec-
tion against decay damage for wood members located
in certain locations.
For those portions of a wood-framed structure that
are subject to damage by decay, the code mandates
that the lumber be pressure-preservatively treated or
be of a species of wood having a natural resistance to
decay.
Crawl spaces and unexcavated areas under a build-
ing usually contain moisture-laden air. These spaces
are required to be ventilated in accordance with Sec-
tion R408 to remove as much moisture as possible be-
fore it causes decay. Wood placed a minimum speci-
fied distance above grade in unexcavated under-floor
areas or crawl spaces as shown in Commentary Fig-
ure R319.1(1) is not required to be either treated wood
or wood that is naturally decay resistant. These clear-
ances below floor joists and beams are deemed to be
the minimum necessary to allow adequate circulation
and removal of moisture from the air and from the
wood framing members. Such clearances apply within
the exterior wall line of the building foundation.
Foundation walls will absorb moisture from the
ground and by capillary action move it to framingmem-
This section addresses the need for minimum protec-tion against decay damage for wood members located
in certain locations.For those portions of a wood-framed structure that are subject to damage by decay, the code mandates that the lumber be pressure-preservatively treated or be of a species of wood having a natural resistance to decay.
Part 2 address "
when closer than 8""....
Part 3 addreses only the situation of a slab on grade, it does not apply to windows or doorway above grade such as the first and second floor of an ICF building.
because it is more than 8" above grade!!
Part 5 addresses
the 6" rule for siding and sheathing.....
For years I also thought "anything wood" in contact with concrete or masonry had to be PT, I was wrong!! These
stipulations clarifying exactly when PT is required is one of the most misapplied applications in regards to code approved work.