Hello Tonya,
Be careful! The strength of SIPs are directly related to the strength of the materials they are made from. OSB that is APA rated structural I has a strength measurement (modulus of rupture) of about 19.5 MPa (mega pascals), or about 2,800 psi (lbs. per sq. inch). The area (sq. inch) is measured as the cross section area of the OSB sheet, so if a sheet of OSB is say, 8' wide and 7/16" (11.1 mm) thick the area would be 42 sq. inch and the estimated point of failure would be about 117,600 lb force, or as commonly reported in the industry 14,700 lbf per linear foot. If the SIP is to be made from OSB of the same specification but is only 5/16" (7.9 mm) thickness then the cross sectional area for the same 8' wide sheet of OSB is now only 30 sq. inch. resulting in an estimated point of failure of 10,500 lbf per linear ft. (more than a 28% decrease). Most manufactures use a load limit (factor of safety) of about 1/3 of the point of failure (4,900 and 3,500 lbf per linear ft. respectively). (In reality there is a lot more to this factor of safety thing, but it gets a bit technical).
A note of prudence would be appropriate here. Estimated point of failure values are no substitute for testing and verification. In short quality demands basic and continuous testing.
Most manufactures base there span tables on data measured or derived from the type of information we have just discussed; hence my warning, be careful, if you do not change your span tables to reflect the change in the materials you construct your SIPs from, you could be headed to-ward's a rocky shore!
Good luck,
Matt B. Phelps, P.E.
SIP Engineering and Testing, LLC