Posted By the_glassman on 10/21/2008 9:20 PM
Should I just demand that they do what I originally wanted and mount the meter on the outside and run the wire through the trusses and down through one of the interior walls in the house into the basement?
In case you're not aware of it, if you do this you will need to have a service disconnect at the meter, or on the wall directly opposite the meter. You can then put the breaker panel wherever you want, with some limits such as not in bathrooms. Service disconnects are pricey. I ran about 100' additional service cable inside 3" conduit outside of the house for what it would have cost to put a service disconnect at the meter and run 70' of 125 amp and 30' of 70 amp service entrance cable inside the house. The two options I was looking at was the meter with disconnect only 30' from the street side junction box with one each 70 and 125 amp panels in the house, or 130' with 200 amp panel with 200 amp main breaker in the garage feeding a 70 amp sub panel in the utility room. The 130' option was the cheaper.
Cost is why the electrician wants to put the breaker panel directly opposite the meter. You can run a lot of #12 wire inside the house for what it will cost to separate the meter and breaker panel by more than 5 to 10 feet. 200 amp main breakers which are purchased separately from a 200 amp breaker panel are very pricey!
Your least costly approach may very well be to put the main breaker panel on the outside wall and run a single larger cable, such as 70 or 100 amp, to a sub panel in the basement. The sub panel would serve your heating equipment and other loads in that area of the house. However, breakers above 70 amp get pricey. You can buy a lot of wire for the price of a 100 amp breaker!