Posted By chuck07 on 11/25/2008 9:51 PM
CFL-IF,
This is helpful info on where to place the HRV for mixing however I was wondering how being placed at the far end of the return helps equalize pressure from a bathroom vent. I didn't think you put return plenums in a bathroom.
I think he was saying he doesn't use an HRV; he just uses a plain outside air intake. This will pressurize the whole house (very slightly) when the air handler fan runs and brings in air through that intake. When the air handler fan does not run, no air comes in. Outside air will come into bathrooms via the supply registers in the bathrooms (which are connected to the return via the air handler, and the intake via the return), or else through undercut doors or jump ducts or whatever, and if the bathroom is depressurized enough it will even suck air through that intake (via supply ducts) when the air handler fan is not running. Ditto for kitchen exhaust fans.
The problem with this setup is that the amount of outside air you get is proportional to the amount of heating or cooling you're doing, because you only get outside air when you heat or cool. (Unless you run the fan continuously.) But in fact, the times when you're not doing a lot of heating or cooling is exactly when you want the most outside air, because that's when the weather outside is nice. The best thing in this case is to get an air handler with an ECM blower, which can run continuously at very low speed efficiently, so that you get a little bit of ventilation and circulation all the time. (A standard non-ECM blower will consume a fair amount of power if you run it continuously, plus it will be moving air faster than you probably want it to.)
I'm not sure why he thinks it needs to be at the far end of the return duct system. I've usually seen it done right before the return air enters the air handler, and just before the central air filter if one is installed. (And central filters are a very good idea, so long as the homeowner remembers to change them before they clog up and burn out your blower motor.)