Posted By thomassargent on 01/20/2010 8:12 PM
Thanks for the reply, but... I was asking about problems with materials and the validity of the concept, considering I felt it odd that the topic had not been covered before in this forum or on the internet (that I could find anyway). If, through this venue and others, I determined it was the best solution for the given situation I would apply heating load and other design calculations. Obviously in a 25 square foot bathroom not all of the floor will be heated (none under the bathtub, toilet, vanity, linen closet). Before you go calling someone a hack perhaps you should inquire a little deeper. Comments like that really undermine the usefulness of a great site like this and my desire to post what I believe are useful and relevant questions.
-Thomas
To be clear, I wasn't calling
you a hack, only pointing out that design-by web-forum without the fundamental data to work with is in the realm of guesstimating/hacking/hoping that it's "about right", and that this project is more complicated than separately controlled micro-zone.
From the nature of the questions (and the fact that you've specified neither the water temp & flow, nor the heat load of the room) gives me the sense that the necessary math on the hydronic design isn't being done. By referring to designing rather than hacking, I'm only strongly encouraging you (or anyone) to learn all you can about hydronic & radiant design before installing it. Were it a micro-zone (which it isn't) with it's own controls, the design would be a lot more forgiving (you can often over-design the radiation capacity by several fold and let the controls dial it back without discomfort.) But if I understand this correctly, you need to balance the radiation of the bathroom with the radiation on the rest of the zone, which makes it a different problem (to be solved with a sharper pencil.)
Yes, it can be done, yes PEX can take the heat, but that's not even the beginning.
Hell, I do hacks all the time (and usually get away with it), but this is one I'd want to be very careful about. Does that make me a hack? (Yeah, well, kinda- just ask Morgan or Rob!
)
Now, in the spirit of HACKING this together at indeterminate water temp without mixing valves...
(and mind you, this isn't a recommendation- it's a hack...)
...I'd plumb it with a section of 1" copper in parallel with a 2-loop manifold/balanced-length pair of 1/2" PEX under the floor, with separate ball valves on both the parallel stub and the radiant side to be able to control the flow to to the radiant. As a design methodology it sucks, but you'd at least have a chance at tweaking it after the fact, and wouldn't likely (TBD) be adding so much head to the zone pump that the system stalls/can't deliver enough flow to deliver design-day heat to the zone.
You'd still need to ball park how many BTUs/square foot it needs to deliver on design day, determine whether that ends up being foot-frying misery for floor temps at that load (in which case you'd need to provide for supplemental radiation, like a heated towel rack or section of cast-iron baseboard or something), and have a plan for getting at LEAST that much heat out of the tubing & into the floor at whatever temperature you need to run the water to the baseboards on the rest of the heating zone (if it can't do it suspended-tube, figure out how to plate it- possibly above the subloor WarmBoard style- but that could be a hazard in high-temp operation.) That's about as crude a hack as might actually work...
If you're running 180F water the flow though the radiant will be pretty low, with hot-spots on the floor and a big delta-T. If the entire heating system can be run at 140F or lower it'll be higher flow & a more even temp across the radiant. (Not to mention the system as a whole saves ~3% in fuel for every 10F you can drop the temp, which is why outdoor reset control can often save high-single-digit or even low double-digit percentages in fuel, even systems with high-temp baseboards & cast-iron boilers. But I digress...)
You don't mention what boiler you have, or whether it's either inherently (or plumbed to be) low-temp tolerant (w/boiler bypass or something), but most real-world systems are oversized/overdesigned, and can be run cooler & more efficiently than the day they went in. (Pros are often in the habit of hacking it too, eh?)