NRT.Bob,
Can you shed some light on an issue I have with my HVAC man? I'm getting ready to build an ICF house, 2200 sq ft inside the walls, using Roth radiant panels in the floor. I did a heating/cooling load calculation using the "HVAC for Concrete Houses" s/w from the Portland Cement Assoc. I come up with a heat/cool load at 19,000/17,000 BtuH.
My HVAC man, a nephew-in-law, uses the WrightSoft suite. I was going over his calcs yesterday with him at his office, and everything seems correct with his inputs, meaning the window data, wall sizes, roof type & orientation, etc is the same as I used. I was almost shocked at the detailed inputs WrightSoft has. However, he is coming up with a heat/cool load of about 40,000/24,000 BtuH. The cooling isn't way off from my calc, but his heat load is double.
I noticed that the WrightSoft program doesn't have a clear option for sealed conditioned crawlspace (built-in in the PCA program) nor for conditioned attic with insulation on the roof. Stan input a conditioned basement of 4' height, and a vaulted ceiling option that somewhat equates to insulated roof. One thing that has me scratching my head is WS says I have inadequate exposure diversity (AED). I have a hard time understanding that one since I have a lot of roof shading on sw facing windows. But that wouldn't impact the heat load side of the equation a whole lot anyway, I don't think.
Any ideas why there might be such a descrepency between the two programs? Could it be, as PCA touts, that Manual J does not adequately account for the thermal mass of the concrete and the time delay in the heat transfer from out to in, which the PCA program does? The fact that WrightSoft is no slouch of a program, and that it is so different from the PCA result, really has me puzzled.
Would it worth the $50 to buy the one time use of HVAC-Calc for a comparison? I used it a couple of years ago for an AC replacement. It worked good, but that was on a frame constructed house.
The PCA s/w heat load is in line with what I have heard or read commented about in other ICF houses.
Posted By NRT.Rob on 04/28/2007 11:45 AM
Hi Clay,
Those are both pro-caliber programs, but two things come to mind. To be clear about my bias, I design radiant heating systems for a living, so take that for what it's worth.
1. GIGO, garbage in, garbage out. If you know something about heating or hydronics you might be ok, but these are just programs to help a knowledgable person do a design.. if you are not knowledgable, it is still possible to make big mistakes during the load calculation or in decisions after that.
2. That is a very expensive software suite (wrightsoft). It's very good, probably the best or one of the best, but you're going to pay for it, for sure.