I'm assuming the system (& backup elements?) is using a combined total of 6.5W. When its in the 20s F the heat pump portion's COP is still greater than 1, probably ~2 at 30F so if it's running constantly your actual peak heat load is probably around 6-8KW, ~5kw of heat pump output, the rest from the resistance elements. (Which would be credible at 25-30F with typical FL insulation levels for an 800' house.) If it's running constantly and barely keeping up (or needing supplemental heat),it means yes, it's using the whole 6.5KW.
Electric boilers aren't outrageous in cost, but your average heating bill will be significantly higher using any type of resistance heater (space heater, HW tank or space heater compared to the heat pump, which probably has a COP of 3+ when it's in the 40s & 50s out. To run at the same or better efficiency as the air heat pump you'd be looking at a hyrdonic heat pump.
With a radiant floor insulated to ~R20 from the crawlspace below your heat loss will be lower. It's usually best to seal & insulate the walls of the crawlspace converting it to semi-conditioned space, which gives you the earth-coupling benefit of the thermal mass below, in which case you can insulate under the radiant to ~R12-ish. Insulating the floor/crawlspace will likely cut the total heat load by at least 10%, possibly as much as 20% (depending on the ventilation rate of the crawlspace as-is.), so a 4.8KW water heater and a pair 1.5KW space heaters probably WOULD keep up (but you'd have to skip the AM shower), but at 2-3x the operating cost of supporting the heat load with heat pumps.
Simply sealing and insulating the crawl space walls may be sufficient to quell the ice-cold floor situation, and would reduce the AC load in summer. Subsoil temps in FL are pretty warm (mid to high 60s F in most places), and the floor temp just coasting would be somewhere between the subsoil temp & room air temp. If it's currently a ventilated crawl, the floor temp is somewhere between room temp and outdoor temp on chilly nights, likely ~50F (or even lower on a really cold night). If insulating the crawl cuts the heat load by 20% the duty-cycle of the heat pump will drop significantly while raising the cold night air temp 10F or more. I'd start there first (2" XPS rigid-board glued to the foundation walls caulked/taped at the seams, held in place with furring strips through-screwed into the foundation, and foam sealed the top. Block any ventilation/windows. Insulate the sill & band joist with the same materials, and lay down at least a 6mil poly vapor retarder, sealed at XPS, mastic sealed at any poly seams with 12" of overlap on the joined sheets. Alternatively, use 2" of closed cell foam in place of the XPS. )
If the floors still feel cold, then would be the time to consider a radiant floor. From an installation cost POV it may be cheaper to use a low-voltage electric radiant system than hydronic pump, heat exchanger, tubing, heat transfer plates, etc. but priced it both ways. Operating costs would be the same- it's electric resistance heating, more expensive to run than heat pumps. |