jbaron
| 24 Jan 2010 01:49 PM |
I'm going to be installing radiant floors in two bedrooms using ThermalBoard. The bedrooms are on top of one another, and the lower one is over a basement.
The upper bedroom is slightly smaller, but the heat loss is higher, because of a bit more glazing and the surface area of the roof, primarily.
Both bedrooms will be using the same temperature water. If I install the ThermalBoard on the entire floor areas of both bedrooms, the lower bedroom, having a lower heat loss but more surface area, will cycle more often.
It seems like I could take a leap, trust my calculations, and omit some of the ThermalBoard in the lower bedroom.
What do you think?
Jeff |
NRT.Rob
| 25 Jan 2010 08:40 AM |
you could probably balance the flow down as well.
that said you probably don't want to zone rooms on different floors together. that's a bad idea. |
jbaron
| 25 Jan 2010 09:44 AM |
Rob,
I'm not going to zone the rooms together; sorry that I gave you that impression. My only real question is "is it worth it to decrease the amount of tubing on the floor to get what I think will be a more consistently-on zone? Or, shoudl I take my on-off cycling and not worry about it?"
Jeff |
NRT.Rob
| 25 Jan 2010 09:45 AM |
use a floor sensor and forget about it :D
or flow balance. I would not do partial floor coverage. |
jbaron
| 25 Jan 2010 09:59 AM |
OK THEN!!! Thanks Rob. What kinds of thermostats would be useful here, then?
Jeff |
NRT.Rob
| 25 Jan 2010 01:23 PM |
we like the tekmar 508's as a good, standard duty thermostat with logic and a floor sensor input. |
jbaron
| 25 Jan 2010 05:02 PM |
Thanks Rob.
Jeff |