Please excuse this newbie question:
My helper was a little hasty with nipping the zip ties and put a nick in the pex. I really don't want to have any couplings in the concrete, and am considering tearing this loop out and just replacing it. Is this over kill, how trustworthy is a crimp repair?
I've attached a pic. The damage is rather minimal and the tubing is holding pressure, but I feel it would be irresponsible to leave this be. What would you do? |
Attachment: pex.jpg
|
|
|
|
|
|
mikeinnyc
 New Member
 Posts:47
 |
| 18 Sep 2010 07:35 PM |
|
REPLACE!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!! OR PAY LATER!!!!!!!!!!!!!! |
|
| MIKE IN NYC |
|
|
mikeinnyc
 New Member
 Posts:47
 |
| 18 Sep 2010 07:36 PM |
|
NO O2 BARRIER????????? RED COLOR |
|
| MIKE IN NYC |
|
|
Blueridgecompany.com
 Advanced Member
 Posts:656
 |
| 18 Sep 2010 10:57 PM |
|
crimp couple, air test 50 psi, soap test, tape over joint to prevent concrete contact with joint. move on be more careful. Dan |
|
| Dan <br>BlueRidgeCompany.com |
|
|
Zeke
 New Member
 Posts:4
 |
| 19 Sep 2010 05:11 PM |
|
Thanks for the replies. I ended up replacing that loop, there's enough undamaged length for a staple up bathroom loop on my upper floor. Mike: it is O2 barrier, from ThermaPex. Dan: I did pick up some crimp couplings, but given I had some extra time (concrete guy is off schedule) I just figured I'd replace. Believe me, I'm being careful. My helper (father, god bless him) is sometimes a little eager. |
|
|
|
|