Sorry I was so late to the party - been away from the forum for a while. Go to this link: http://www.thermalboard.info/pdfs/ThermalBoard_inst-app_manual.pdf. The recommendations for tile are on page 23. You CAN put backer board over Thermalboard. You can also use thinset as described in the manual. My personal experience is that you can also thinset below the backer, as many tile folks recommend, in order to fill any irregularities and level the backer board. Thinset won't hurt the aluminum or the PEX, and as NRT.Rob noted, it is inert once set. While its performance does not match Warmboard's, only your heat loss calcs can tell you whether it will be sufficient for your application. Water temps may need to be raised or lowered. Get a heat loss, use the recommended temperatures from the manual, then fiine-tune as needed to prevent over-cycling or under-performing. NOTE: Although this is not an authorized response from Thermalboard or Zurn, I believe you can dispense with the anti-fracture membrane when using thinset, provided you have a solid subfloor assembly below with no deflection. The backer board and thinset will protect against the delta of expansion between the tile and the subfloor/thermalboard. As for the MDF concerns about moisture, yes, you must protect it from moisture during the process. If you set the tile and edging properly, moisture shouldn't be a concern going into the future. For plumbing leaks, it won't be as forgiving as plywood if it ever does get wet later, but it shouldn't get wet if everything is done properly.
|