I'm trying to figure out what size water heater I would need to meet both Heat Load and DHW load. This is for a new house and design heat load is ~36 000 BTU/hr. I am installing radiant heat in thin slab in the floors. The thing I don't know how to factor in is DHW load. If I do sizing for DHW I would need a standard dual element 5500 watt 60 Gal tank. My plan was to use a 5500W dual element 60 gal tank but change the elements to non flip flop operation. This would give me 11KW of power. Is that enough? BTW my only choice is electric.
NRT.Rob
Veteran Member
Posts:1741
11 Jan 2011 10:32 AM
No, it's not. You need an electric boiler. a 36,000 BTU/hr load is just about 11kw by itself.
Rockport Mechanical<br>RockportMechanical.com
Rosalinda
Basic Member
Posts:353
11 Jan 2011 01:49 PM
Sorry if this is an inane question, but you can't get propane?
Sum total of my experience - Designed, GCed and built my own home, hybrid - stick built & modular on FPSF. 2798 ft2 2 story, propane fired condensing HWH DIY designed and installed radiant heat in GF. $71.20/ft2 completely furnished and finished, 5Star plus eStar rated and NAHB Gold certified
BadgerBoilerMN
Veteran Member
Posts:2010
11 Jan 2011 06:02 PM
Rob is right.
It is not wise to get creative with approved appliances.
Electric boiler with reset and a Marathon water heater sized to the load and conditions e.g. off-peak.
Your radiant floor designer should help you with this.
MA<br>www.badgerboilerservice.com
ANGELofDEBT
New Member
Posts:60
13 Jan 2011 09:12 AM
Ok so I guess I'll rephrase my question. How would I go about sizing a tank water heater for combination use. It's done with propane tank heaters so if I size the water heater properly shouldn't it work the same. I can get a light industrial build to order anywhere in the 6-54 KW range (21 000- 190 000 BTU/hr). The reasoning for a single heat source was to add solar to it later on.
BadgerBoilerMN
Veteran Member
Posts:2010
13 Jan 2011 10:16 AM
You will need a tank and heat exchanger for solar. Depending on your climate you can expect 50 duty load (saving about $25/month here in Minneapolis). The whole system must be designed as one before you start.
MA<br>www.badgerboilerservice.com
NRT.Rob
Veteran Member
Posts:1741
13 Jan 2011 10:39 AM
You probably don't want a tank if you're going to add a solar tank later.
Rockport Mechanical<br>RockportMechanical.com
You are not authorized to post a reply.
Green Building Forums
--General Forum - Residential
--General Forum - Commercial
--Green/Energy-Efficient Design and Planning
--Green/Energy-Efficient Building and Construction
Green Building Technologies
--Insulating Concrete Forms (ICFs)
--Structural Insulated Panels (SIPs)
--Radiant Heating
--Geothermal Heat Pumps
--Solar and Wind Power
--Windows/Doors and Interior/Exterior Finish
--Appliances, Lighting and Kitchen/Bath Fixtures
Feedback/Support
--Rules, Instructions and Announcements
--Suggestions/Feedback
--Testing Area
Forums
>
Green Building Technologies
>
Radiant Heating
Active Forums 4.1
Membership:
Latest:
croccohvacusa
New Today:
0
New Yesterday:
0
Overall:
35027
People Online:
Visitors:
348
Members:
0
Total:
348